Vsd, Installation
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
bob14
post Nov 29 2009, 10:38 AM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 12
Joined: 16-December 08
Member No.: 5,027



Hi,

We are planning to install a dozen of VSDs, 7.5 kW 400 V, on a new site. The panel powering the VSDs are loaded with a power factor correction capacity bank. The bank is permanently powered. Having been through the forum, I am wondering how the local capacity bank could affect the performance of the VSDs. The VSDs are of the Siemens micomaster type.
Thanks.

Bob


Go to the top of the page
 
+Quote Post
marke
post Nov 29 2009, 05:45 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Bob

When you say that the capacitors are permanently powered, I assume by that you mean that they are not switched at all. This is most unusual!!

The action of the capacitors will be to amplify transients which could be enough under some conditions to damage the inputs to the VFDs, and also to increase the transient fault current so that the VFDs, when hit by a line transient, are more likely to be damaged due to the current magnitude.

I would recommend fitting AC line reactors if the capacitors are closer than 50M in cable length from the VFDs.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
AB2005
post Nov 30 2009, 04:09 AM
Post #3


Senior Member
*****

Group: Full Member
Posts: 277
Joined: 21-October 06
Member No.: 2,159



QUOTE (marke @ Nov 29 2009, 10:45 PM) *
I would recommend fitting AC line reactors if the capacitors are closer than 50M in cable length from the VFDs.

Best regards,
Mark.


Hello Mark,

Great info. But if capacitors are switched through PF controller then?? It too need to install line reactor under such installation?



--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
marke
post Nov 30 2009, 08:16 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello AB2005
Yes, the act of switching the capacitors creates transients and the low impedance causes the transient currents to be high enough to cause problems.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 




RSS Lo-Fi Version Time is now: 16th March 2010 - 02:21 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers