earth wire size fro motors |
![]() ![]() |
earth wire size fro motors |
Oct 22 2002, 09:41 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 11 Joined: 29-August 02 Member No.: 70 |
how to calculate the SWG for earth wire , it also depend on load ?
some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail |
|
|
|
Oct 23 2002, 06:06 AM
Post
#2
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 42 Joined: 28-June 02 From: Melbourne, Australia Member No.: 26 |
Hello tahira,
In general, the earth conductor should be large enough to 'safely' carry the prospective short circuit current. This really means that the earth conductor must be of sufficient cross sectional area to safely (ie without excessive temperature rise) carry the short circuit current until the branch protection device (ie circuit breaker/fuse) clears. In practice, how do you apply this information? Here in Australia, I would refer to Australian Standard AS3000, which lists common Active conductor sizes with minimum applicable Earth conductor sizes. In general, the size ratio varies by between 30-50% or so. Unfortunately there is no simpe fixed ratio. An alternative (and more complex, as per AS/NZS3008) approach is to calculate the size required based on prospective short circuit currents, expected fault duration and protective device clearing times. Most of this information is not readily available, therefore reference to AS3000 is easier (for me). My suggestion therefore would be to refer to your local standards. I hope this is helpfull. BigMax |
|
|
|
Oct 24 2003, 03:38 AM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 24 Joined: 7-October 03 From: houston Member No.: 514 |
In the USA we call it the "equipment grounding conductor". Its size ,is as stated above, is based on the OCP (over current protection) on the phase conductors serving said equipment. We follow table 250.122 from the NEC to size the ECG.
|
|
|
|
| Guest__* |
Feb 6 2004, 12:18 PM
Post
#4
|
|
Guests |
QUOTE Originally posted by tahira
how to calculate the SWG for earth wire , it also depend on load ? some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail |
|
|
|
Feb 6 2004, 12:23 PM
Post
#5
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 5 Joined: 5-February 04 Member No.: 644 |
QUOTE Originally posted by tahira
how to calculate the SWG for earth wire , it also depend on load ? some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail 50% of your current load |
|
|
|
| Guest__* |
Sep 15 2004, 03:55 PM
Post
#6
|
|
Guests |
the earth as to be half the conductor size over 16mm
|
|
|
|
Jan 21 2007, 06:50 PM
Post
#7
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 9 Joined: 14-June 05 Member No.: 1,127 |
I disagree ....the earth wire should be greater or equal to the current carring conductor... It should offer less resistance to the flow of current or the fault current might take a different path ...
|
|
|
|
Jan 22 2007, 02:13 AM
Post
#8
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Full Member Posts: 221 Joined: 21-October 06 Member No.: 2,159 |
Hi Tahira;
We are working at a new project and following JAAKKO POYRY standards. We also select the main earth conductor for machines the half size of power cable. If power cable is, for example, 120mm˛, then we select 70mm˛ earth conductor. -------------------- "Don't assume any thing, always check/ask and clear yourself".
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
4 | Itos | 1,952 | 24th June 2002 - 04:02 AM Last post by: Itos |
|||
![]() |
1 | Itos | 1,575 | 26th June 2002 - 08:56 PM Last post by: marke |
|||
![]() |
8 | marke | 2,909 | 20th October 2004 - 06:56 PM Last post by: marke |
|||
![]() |
1 | -ksvs29- | 1,654 | 15th August 2002 - 09:22 PM Last post by: marke |
|||
![]() |
0 | GGOSS | 1,600 | 12th August 2002 - 08:28 AM Last post by: GGOSS |
|||
|
Lo-Fi Version | Time is now: 4th December 2008 - 03:14 AM |