how to calculate the SWG for earth wire , it also depend on load ?
some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail
Go to the top of the page
 
+Quote Post
BigMax
post Oct 23 2002, 06:06 AM
Post #2


Intermediate Member
***

Group: Full Member
Posts: 42
Joined: 28-June 02
From: Melbourne, Australia
Member No.: 26



Hello tahira,

In general, the earth conductor should be large enough to 'safely' carry the prospective short circuit current. This really means that the earth conductor must be of sufficient cross sectional area to safely (ie without excessive temperature rise) carry the short circuit current until the branch protection device (ie circuit breaker/fuse) clears.

In practice, how do you apply this information?

Here in Australia, I would refer to Australian Standard AS3000, which lists common Active conductor sizes with minimum applicable Earth conductor sizes. In general, the size ratio varies by between 30-50% or so. Unfortunately there is no simpe fixed ratio.

An alternative (and more complex, as per AS/NZS3008) approach is to calculate the size required based on prospective short circuit currents, expected fault duration and protective device clearing times. Most of this information is not readily available, therefore reference to AS3000 is easier (for me).

My suggestion therefore would be to refer to your local standards.

I hope this is helpfull.

BigMax
Go to the top of the page
 
+Quote Post
grobert
post Oct 24 2003, 03:38 AM
Post #3


Intermediate Member
***

Group: Members
Posts: 24
Joined: 7-October 03
From: houston
Member No.: 514



In the USA we call it the "equipment grounding conductor". Its size ,is as stated above, is based on the OCP (over current protection) on the phase conductors serving said equipment. We follow table 250.122 from the NEC to size the ECG.
Go to the top of the page
 
+Quote Post
Guest__*
post Feb 6 2004, 12:18 PM
Post #4





Guests






QUOTE
Originally posted by tahira
how to calculate the SWG for earth wire , it also depend on load ?
some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail
Go to the top of the page
 
+Quote Post
jhun
post Feb 6 2004, 12:23 PM
Post #5


Junior Member
**

Group: Members
Posts: 5
Joined: 5-February 04
Member No.: 644



QUOTE
Originally posted by tahira
how to calculate the SWG for earth wire , it also depend on load ?
some body tell me the general rule i.e earth wire size half the cables used for equipment.plz tell me in detail




50% of your current load
Go to the top of the page
 
+Quote Post
Guest__*
post Sep 15 2004, 03:55 PM
Post #6





Guests






the earth as to be half the conductor size over 16mm
Go to the top of the page
 
+Quote Post
porky
post Jan 21 2007, 06:50 PM
Post #7


Junior Member
**

Group: Full Member
Posts: 9
Joined: 14-June 05
Member No.: 1,127



I disagree ....the earth wire should be greater or equal to the current carring conductor... It should offer less resistance to the flow of current or the fault current might take a different path ...
Go to the top of the page
 
+Quote Post
AB2005
post Jan 22 2007, 02:13 AM
Post #8


Senior Member
*****

Group: Full Member
Posts: 221
Joined: 21-October 06
Member No.: 2,159



Hi Tahira;

We are working at a new project and following JAAKKO POYRY standards. We also select the main earth conductor for machines the half size of power cable. If power cable is, for example, 120mm˛, then we select 70mm˛ earth conductor.


--------------------
"Don't assume any thing, always check/ask and clear yourself".
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 Itos 1,952 24th June 2002 - 04:02 AM
Last post by: Itos
No New Posts   1 Itos 1,575 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   8 marke 2,909 20th October 2004 - 06:56 PM
Last post by: marke
No New Posts   1 -ksvs29- 1,654 15th August 2002 - 09:22 PM
Last post by: marke
No New Posts   0 GGOSS 1,600 12th August 2002 - 08:28 AM
Last post by: GGOSS



RSS Lo-Fi Version Time is now: 4th December 2008 - 03:14 AM
hosted by : L M Photonics Ltd