Junior Member ![]() ![]() Group: Full Member Posts: 9 Joined: 14-June 05 Member No.: 1,127 |
Please advise on why some motors are limited to several starts per hour....
Is it due to fear of Overheating the windings due to high inrush current or is it ti prevent mechanical damage to motor and or pumps. |
|
|
|
Jun 24 2005, 06:54 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi porky
There is a thermal limit on the motor that determines the life expectancy. During start, the kinetic energy of the load at full speed is disipated in the rotor, plus there is a high dissipation in the stator. The temperature rise in the rotor is dependant on the load kinetic energy at full speed. The end temperature of the rotor is dependent on the prestart temperature and the temperature rise during start. It takes a long time for the rotor to cool, so if you start too regularly, you will over heat the rotor. If you start a machine with too much inertia, you will also overheat the rotor. Strictly speaking, the starts per hour should be quoted at a particular load energy. If you start a lighter duty load, you should be able to start more often. Additionally, the end temperature is going to be affected by the ambient temperature, so there is more thermal capacity if you are starting with an ambient temperature of 0 degress than if you are starting with and ambient temperature of 50 degrees. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jun 25 2005, 10:13 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 9 Joined: 14-June 05 Member No.: 1,127 |
Just a quick thanks for the info...
|
|
|
|
Jul 20 2005, 09:41 AM
Post
#4
|
|
|
system($cmd); ?> ![]() Group: Members Posts: 1 Joined: 19-July 05 Member No.: 1,161 |
explain the physical phenmenom in rotar circuit during starting.
-------------------- saleem
|
|
|
|
Jul 20 2005, 10:30 AM
Post
#5
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello saleem
I am not sure what you are looking for. There is no change in the rotor during start, there is power dissipated in the rotor bars and this causes the rotor bars to heat up. Can you please explain your question in more detail. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
32 | marke | 13,768 | 28th March 2008 - 01:02 PM Last post by: lau |
|||
![]() |
2 | GGOSS | 2,954 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
0 | marke | 3,390 | 11th June 2002 - 10:32 PM Last post by: marke |
|||
![]() |
0 | marke | 2,665 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
0 | marke | 2,249 | 11th June 2002 - 10:42 PM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 4th December 2008 - 03:46 AM |