Hi
How can I solve the harmonic and resonance problems when I am dealing with the power factor correction? Could anyone tell me the principle and steps of switching the capacitor to correct the power factor precisely? Thanks a lot. Lewis |
|
|
|
Oct 8 2002, 08:33 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Lewis
The harmonic currents in the capaciotrs can be reduced by using detuning capacitors. The automatic selection of capacitors is achieved by the use of a power factor control relay. This measures the power factor. If the power factor is less than a preset level, (typically 0.95) it connects another bank and continues to add banks until the power factor is high enough. If the power factor becomes capacitive, the relay begins to shed banks until the measured power factor is in a suitable band. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Oct 8 2002, 11:24 AM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 16 Joined: 27-September 02 Member No.: 109 |
Hello Marke
Sorry, could you explain more about the detuning inductors? Any other methods or techniques can improve the power factor, harmonics and the effect of resonating at the same time? Active filters or passive filters can improve it? Thanks Lewis |
|
|
|
Oct 8 2002, 05:53 PM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Detuning reactors are just inductors added in series with the capacitors to provide a series tuned circuit of somewhere between 100 and 250 Hz. Typically 189Hz on a 50Hz system for a 7% reactor. This results in an inductive system above resonance and thereby reduces harmonic current flow.
The alternative is an active compensator which is essentially an inverter either using series or shunt injection to correct the harmonic currents. This can also provide reactive currents and result in an overall power factor improvment. These systems are expensive at the moment. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | Itos | 1,673 | 26th June 2002 - 08:56 PM Last post by: marke |
|||
![]() |
1 | marke | 2,227 | 2nd November 2006 - 03:23 AM Last post by: AB2005 |
|||
![]() |
1 | Lewis | 1,682 | 28th September 2002 - 01:37 AM Last post by: marke |
|||
![]() |
5 | metro | 1,837 | 10th December 2004 - 12:09 PM Last post by: -Anonymous- |
|||
![]() |
2 | amrh | 2,583 | 2nd July 2004 - 04:56 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 10th January 2009 - 04:01 AM |