protection system
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
tahira
post Nov 30 2002, 09:57 AM
Post #1


Intermediate Member
***

Group: Members
Posts: 11
Joined: 29-August 02
Member No.: 70



Hi gents!

We are recently working on a substation having 132/11kV system with 36MVA transformer (Y-Y with treasery winding). There are differential, O/C, U/V, O/V, E/F and all other transformer protections is there with individual protection for different feeders (S/C, E/F, O/C).

I have following quires:

1. What is the difference b/w unrestricted and restricted earth fault protection, how they differ and what are there selecting criteria according to application, which one provided more accurate and complete protection?
2. What is the setting procedure for differential protection?
3. Selection criteria of protection relays setting i.e. O/V, U/V, O/C and S/C.
4. What is directional O/C relay, how they differ from no directional relay, is there any advantage for using directional relay?
5. Plz info me any web site given me details about protection relays (cables feeder protection, …)?
6. Is any one having info about E-Tap software?


Best regards
ASD
Go to the top of the page
 
+Quote Post
jackson8000
post Jan 19 2003, 06:53 PM
Post #2


Junior Member
**

Group: Members
Posts: 3
Joined: 18-January 03
Member No.: 246



Hello tahira,

Regarding item #6, ETAP software is very good. We use it exclusively for analysis, coordination, etc. You can find it at www.etap.com. Good luck.
Go to the top of the page
 
+Quote Post
RalphChristie
post Mar 21 2003, 01:09 PM
Post #3


Intermediate Member
***

Group: Members
Posts: 30
Joined: 8-November 02
From: Northern Cape, South Africa
Member No.: 168



I would suggest that you visit following sites

http://www.geindustrial.com/pm/notes/artsci/ - go to transformer protection
http://www.selinc.com/techpprs.htm
http://www.ee.polyu.edu.hk/staff/eekkli/BE.../Ch3_OC2003.pdf - very good - about relaying
http://www.usace.army.mil/inet/usace-docs/...ytm/tm5-811-14/

http://www.relaylounge.com/servlet/Content...id=987664718399
For last one you have to register (free) - then go to NPAG relay technology

It is a lot of places - but there is good information

Good luck
RCC
Go to the top of the page
 
+Quote Post
sethar
post Aug 22 2003, 09:01 AM
Post #4


Junior Member
**

Group: Full Member
Posts: 8
Joined: 31-July 03
From: karachi
Member No.: 438



Hello tahira,

1. Unrestricted earth fault is used for feeder protection,not for limited zone & less sensitive. Restricted earth fault is used for transformer protection ,it is also called ground diffrential & limited to zone , not will trip beyond the zone.
Restricted is more accurate protection.
2. Setting procedure of diffrential depends on both side Pri/Sec current & CT ratio ( Suppose in case of transformer Delta to Star)
Star side I = 1600 A & CT is 2000/1
Delta side I = 52 A & CT is 75/1
1600/2000=base current
52/75=base current
those settings intered into relay includind system parameters
actually diffrential relay sense ratio/deffrence between both side in term of % according to settings + error in base current ratio, in this relay no any time setting is required it take action on immediate effect as sense diffrence.
3. Selection criteria of protection relays depends system designe/load/criticality /as per current carrying capacity of equipment/short ckt values/i.e down stream side settings should be lower than up stream side.
4. Directional relay is better than withour directional relay it woks/sense through one direction only.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   0 marke 2,856 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   4 GGOSS 1,014 5th September 2002 - 07:45 AM
Last post by: GGOSS
No New Posts   1 -mahesh- 1,754 4th April 2006 - 06:08 AM
Last post by: khongai
No New Posts   0 tahira 706 --
Last post by: tahira
No New Posts   1 normannicklette 1,988 1st November 2004 - 08:01 AM
Last post by: RalphChristie



RSS Lo-Fi Version Time is now: 10th January 2009 - 04:41 AM
hosted by : L M Photonics Ltd