Let me know why we found moisture usually inside the Motor body when dismental for maintenance even specification is EEx de II C T4, IP 55.
Go to the top of the page
 
+Quote Post
jOmega
post Dec 7 2006, 06:48 PM
Post #2


Member
****

Group: Full Member
Posts: 153
Joined: 26-February 06
From: Midwest, USA
Member No.: 1,401



perhaps you would be so kind as to share a bit more information with us.

Like, the environment in which the motor is installed ..... i.e., indoor? outdoor?
( I would guess mtr. is outdoors or in an un-heated building or room) ...


Ambient temperature range to which the motor is subjected ?


How many hours a day does the motor operate ?

How many days a week is the motor operated ?

Is the motor un-powered and un-heated over the weekend ?


Condensation is virtually impossible to keep out of a motor, regardless of construction; especially when it is subjected to wide temperature extremes or is left in an unheated environment for extended periods of time. Typically occurs when the ambient temperature falls below the dewpoint.


Suggestion: Have thermostatically controlled space heater installed in motor. Circuit should be designed so that space heater is energized when motor is not powered.

This will prevent condensation from occurring inside the motor.



--------------------
Go to the top of the page
 
+Quote Post
mariomaggi
post Dec 7 2006, 09:28 PM
Post #3


Member
****

Group: Full Member
Posts: 199
Joined: 15-March 05
From: Milan, Italy
Member No.: 1,068



Dear sethar,

IP55 means that the motor is protected v/s rain, not v/s moisture.

All EEx de motors must have an internal small air duct (lamination) for exaust gases in case of an internal explosion.
Please check also if there is the right quantity of grease near bearing, to improve moisture resistance.

In some application it is accepted a continuour heating during stand-by using the same motor windings, feeded at very low voltage.

Regards
Mario


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 Itos 1,662 24th June 2002 - 04:02 AM
Last post by: Itos
No New Posts   1 Itos 1,428 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   8 marke 2,842 20th October 2004 - 06:56 PM
Last post by: marke
No New Posts   1 -ksvs29- 1,504 15th August 2002 - 09:22 PM
Last post by: marke
No New Posts   0 GGOSS 1,498 12th August 2002 - 08:28 AM
Last post by: GGOSS



RSS Lo-Fi Version Time is now: 7th October 2008 - 03:52 PM
hosted by : L M Photonics Ltd