Dear all,
I have capacitor banks overloaded morethan 130% (as per IEC). What action shall I take?How to rectify?

Kindest regards,
Go to the top of the page
 
+Quote Post
marke
post Apr 3 2007, 07:08 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Riyad

I assume from your post that you are operating the capacitors with the rated voltage and frequency and under those conditions, the current is more than 130% of the rated current.

If this is the case, you have problems with harmonics which will cause the capacitors to fail.

The best solution, is to get rid of the harmonics, but this is not always easy, so the next best solution, is to use detuning reactors.

If you use detuning reactors, you must:
  1. Use capacitors rated for use with detuning reactors. They must be able to sustain a higher voltage continuously. Consult your capacitor supplier.
  2. Use detuning reactors rated in the KVAR of the capacitors on each capacitor or bank. It is important that the KVAR rating of the capacitors and detuning reactor match.
see http://www.lmphotonics.com/pwrfact.htm

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Riyad
post Apr 4 2007, 05:27 AM
Post #3


Junior Member
**

Group: Full Member
Posts: 6
Joined: 19-August 06
Member No.: 1,811



Thank you very much.
Appreciate your reply.



QUOTE(marke @ Apr 3 2007, 10:08 PM) [snapback]5835[/snapback]

Hello Riyad

I assume from your post that you are operating the capacitors with the rated voltage and frequency and under those conditions, the current is more than 130% of the rated current.

If this is the case, you have problems with harmonics which will cause the capacitors to fail.

The best solution, is to get rid of the harmonics, but this is not always easy, so the next best solution, is to use detuning reactors.

If you use detuning reactors, you must:
  1. Use capacitors rated for use with detuning reactors. They must be able to sustain a higher voltage continuously. Consult your capacitor supplier.
  2. Use detuning reactors rated in the KVAR of the capacitors on each capacitor or bank. It is important that the KVAR rating of the capacitors and detuning reactor match.
see http://www.lmphotonics.com/pwrfact.htm

Best regards,

Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   6 Neutron 1,170 23rd March 2005 - 06:56 PM
Last post by: marke
No New Posts   8 -Anonymous- 1,289 11th October 2005 - 11:36 PM
Last post by: oskin
No New Posts   0 dennis3834 33 29th December 2008 - 04:25 AM
Last post by: dennis3834



RSS Lo-Fi Version Time is now: 10th January 2009 - 04:43 AM
hosted by : L M Photonics Ltd