Hi. Just had a 150kW (old type) WEG motor fail due to rotor bars collapsing. Bars are copper section welded at ends. Bars have burnt through laminations at the ends in places. Debris has cut windings. Motor is soft started and drives a high inertial load. Soft start is AB. Start time is 20 secs. Is this just old motor problems or has the high rotor currents flowing for protracted periods caused the rotor bars to overheat The second failure is a 90kW weg motor. In this case the rotor assembly has shifted along the shaft and hit the endbell. Motor is vertically mounted. My beleif this would be a warranty case but motor is 10 yrs old.
|
|
|
|
Apr 23 2007, 07:33 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,086 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello arcserv
When you start a motor, there is a period of time when the motor is accelerating the load from zero speed to full speed. During this time, there are high slip losses dissipated in the rotor. This will cause heating of the rotor bars. Provided that the start current is high enough, the motor will have plenty of acceleration torque and spin freely to full speed. The total power dissipated in the rotor is equal to the full speed kinetic energy of the driven load. A high inertia results in a high power dissipation. If the start current is too low, the motor will struggle to accelerate the load and the power dissipation will be increased. Motors have a maximum load inertia that they can start. This is related to the maximum energy that can be dissipated in the rotor. This can also be rated as maximum start time or max Locked Rotor time. If the motor is inappropriate for the load inertia, or the soft starter not set up correctly, you will have the rotor problems that you describe. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Apr 23 2007, 07:55 AM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 11 Joined: 4-April 06 Member No.: 1,456 |
QUOTE(marke @ Apr 23 2007, 07:33 AM) [snapback]5949[/snapback] Hello arcserv When you start a motor, there is a period of time when the motor is accelerating the load from zero speed to full speed. During this time, there are high slip losses dissipated in the rotor. This will cause heating of the rotor bars. Provided that the start current is high enough, the motor will have plenty of acceleration torque and spin freely to full speed. The total power dissipated in the rotor is equal to the full speed kinetic energy of the driven load. A high inertia results in a high power dissipation. If the start current is too low, the motor will struggle to accelerate the load and the power dissipation will be increased. Motors have a maximum load inertia that they can start. This is related to the maximum energy that can be dissipated in the rotor. This can also be rated as maximum start time or max Locked Rotor time. If the motor is inappropriate for the load inertia, or the soft starter not set up correctly, you will have the rotor problems that you describe. Best regards, |
|
|
|
Apr 23 2007, 08:02 AM
Post
#4
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 11 Joined: 4-April 06 Member No.: 1,456 |
Hi Mark
yes i appreciate your comments. Motor has been in this application for many years and is the appropriate size. The soft start has been set so as to accelorate the motor as quickly as possible and within the starting characteristics of locked rotor start time. This motor has been rewound once and before i changed the soft start it had an overload which was incorrectly sized ie set too high, possibly it has recieved a thrashing. Soft start is AB SMC flex. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
4 | tahira | 1,755 | 20th January 2003 - 07:29 PM Last post by: castera |
|||
![]() |
1 | superabu | 847 | 27th October 2002 - 10:51 PM Last post by: marke |
|||
![]() |
4 | noble | 1,264 | 2nd November 2004 - 07:55 AM Last post by: RalphChristie |
|||
![]() |
2 | incal | 688 | 30th March 2004 - 08:07 PM Last post by: -Anonymous- |
|||
![]() |
1 | sethar | 1,993 | 10th February 2004 - 06:06 PM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 7th October 2008 - 11:47 PM |