IPB


Welcome Guest ( Log In | Register )

 
Reply to this topicStart new topic
Motor's Use As Star Instead Of Delta
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
simple
post Jun 28 2007, 03:42 PM
Post #1



*

Group: Members
Posts: 1
Joined: 28-June 07
Member No.: 3,437



Dear Gentleman

A10 kw motor which is designed to be used as 380 volt Delta.
If iuse this motor by supplying 380 volt in star
Can i save Energy ?

Regards

simple
Go to the top of the page
 
+Quote Post
jraef
post Jun 28 2007, 04:01 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 644
Joined: 22-February 03
From: USA, California
Member No.: 285



No, except that when the motor trips out on overload, you will save a lot of energy because it will not be running!

When you connect it is star, you are effectively reducing the voltage to each winding by the square root of 3, so you are then reducing the torque that the motor can produce by that voltage reduction squared, ending up with 1/3 of the available torque. If your motor was properly sized to do the job it was intended for, it will stall with only 1/3 of its available torque.


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
marke
post Jun 28 2007, 06:32 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,063
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



If you are operating the motor at less than 3KW, then you can connect in star and you will save some of the iron loss, but if you load is less than 3KW, why are you using a 10 KW motor?

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 2,525 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   0 marke 2,672 11th June 2002 - 10:32 PM
Last post by: marke
No New Posts   0 marke 2,115 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   0 marke 1,846 11th June 2002 - 10:42 PM
Last post by: marke
No New Posts   0 marke 1,893 12th June 2002 - 09:24 AM
Last post by: marke



RSS Lo-Fi Version Time is now: 8th September 2008 - 12:38 AM
hosted by : L M Photonics Ltd