Hello,

I'm new to this forum and I was hoping someone might be able to help with a design question. I'm currently trying to specify a medium voltage autotransformer (Korndorfer type) for a 1.1MW water pumping system. The pumps are operating on a high static head the torque speed characteristic is therefore heavily loaded at >85% of rated speed. In order to calculate the reduced voltage which will permit the pumps to start whilst minimising the starting current I've modelled the load torque characteristic and the electrical torque characteristic using the manufacturers equivalent circuit. I've modified the rotor resistance and reacance as a straight line fit between a slip of 1 and operating slip.
As a consequece of this calculation I've noticed that the starting current on the data sheet of 600% x FLC actually comes out at 720% x FLC on a 100% starting voltage when calculated from the equivalent circuit. Whereas I have no real issue with the motor manufacturer modifying a design to achieve this starting current I am now concerned that the properties of the motor supplied for evaluation against other manufactuers data is of questionable accuracy. I am looking at fairly small differentiators so approximate or generic data will not provide the necessary resolution.

Does anyone know if it is reasonable to expect the equivalvent circuit data to accurately match the data sheet or is my approach in simply reducing the equivalent circuit too simplistic (I know there are satuation and inrush issues which I may have completely overlooked)
Should I be concerned with the validity of the data sheet. 600% does seem a remarkably rounded figure?

Thanks for your help

Go to the top of the page
 
+Quote Post
marke
post Sep 28 2007, 06:59 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Matt303

Welcome to the forum.

I personally do not attempt to model the motor as to get an accurate result, you need an accurate model and accurate values to put into the model. I find that this sort of information is very difficult to come by.

I use the manufacturers curves for the motor and the nameplate data, LRC LRT FLC etc and find that from this I can get pretty good results.
I use the Electrical Calculations software that you can download from www.LMPhotonics.com and enter in the curves, along with the load curves and inertia, and generally find that my figures for start current and start time are pretty good.

Have a good day,
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Matt303
post Sep 28 2007, 05:09 PM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 16
Joined: 26-September 07
Member No.: 3,834



Marke,

Thanks for the reply. The interesting point is that of the tw manufacturers under consideration one of them has supplied X and R values and a profile of the values against slip indicating the variance of X and R as a fuction of slip which seems to be more or less a straight line fit, these seems consistent with most of the text book descriptions. Using my model on this manufacturers data set does provide an output closely matching their dta sheet for starting current, the other manufacturers data is qute inacurate however. Unfortunately the inaccurate motor has a better stated performance (no matter how dubious the figures quoted are). The other issue is a very different moment of intertia, both are 4 pole motors on a 50Hz system and both inertia values are quoted in terms of radius i.e. WR2 one is 75kgm2 and the other 25kgm2 which is a bit of an issue for the pipeline surge supression. I think this means one motor is long and skinny and the other short and fat.
I'm uncomfortable about taking these figures at face value becuase I don't believe them and to accept them woud place the other manufacturer at a disadvantage for not quoting unrealistic and overly optimistic data.
The electrial model is only a thevenin reduction of the clasical induction motor model with a locked rotor i.e. allowing for current flow through the magnetising branch. Whereas saturation effects over the fulll speed range could easily introduce inacruacy the initial maximum start current is a fairly simple reduction.
The vendor under scrutiny who are a very major european supplier are looking at the figures currently and I'm waitiing for them to respond in the absence of a resolution I'm inclined to give the data sheet a health warning when providing recommendations.

Thanks again for your advice I'll check out the software

Go to the top of the page
 
+Quote Post
mariomaggi
post Sep 29 2007, 06:17 AM
Post #4


Senior Member
*****

Group: Full Member
Posts: 209
Joined: 15-March 05
From: Milan, Italy
Member No.: 1,068



Mat303,
QUOTE
The other issue is a very different moment of inertia, both are 4 pole motors on a 50Hz system and both inertia values are quoted in terms of radius i.e. WR2 one is 75kgm2 and the other 25kgm2 which is a bit of an issue for the pipeline surge supression. I think this means one motor is long and skinny and the other short and fat.


you don't wrote the nominal power for such motors, we cannot check.
There is another possibility: in one of two specifications someone put wrongly WD2 instead of WR2 (diameter, not radius).

Regards
Mario



--------------------
Go to the top of the page
 
+Quote Post
Matt303
post Oct 1 2007, 01:30 PM
Post #5


Intermediate Member
***

Group: Full Member
Posts: 16
Joined: 26-September 07
Member No.: 3,834



QUOTE(mariomaggi @ Sep 29 2007, 07:17 AM) *
Mat303,
you don't wrote the nominal power for such motors, we cannot check.
There is another possibility: in one of two specifications someone put wrongly WD2 instead of WR2 (diameter, not radius).

Regards
Mario


Mario,

The inertia quoted in both cases refers to the radius definition. I also wondered if the diameter had been used. This would give a factor of 4 however i.e. D=2*R, D^2 = 4*R^2. In this case the problematic motor has a quoed figure of 1/3 of the other. I don't know of any way to calculate this information from the data sheet information. We have a metric based on a large number of motors but this is an impirical calcuation and does not relate to any particular enginering properties. I'ts used by the surge analysis people when having to analyse a pumping systems with limited information. This predicts a value of 75kgm^2 for a 4 pole 1.1MW mtor. The most significant factor seems to relate to the number of poles. For instance it predicts a figure of 25kgm^2 for a 2 pole 1.1MW motor. Initially I thought the vendor may have made an error and quoted a 2 pole machine but they say not and that it is due to the geometry of the machine.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 hotcars 1,388 11th October 2003 - 05:42 PM
Last post by: grobert
No New Posts   3 Lewis 1,605 12th July 2007 - 09:53 PM
Last post by: marke
No New Posts   1 sethar 2,617 10th February 2004 - 06:06 PM
Last post by: marke
No New Posts   0 -Anonymous- 926 20th July 2004 - 07:37 AM
Last post by: -Anonymous-
No New Posts   3 Sandipan 1,584 10th September 2007 - 05:38 AM
Last post by: chinni



RSS Lo-Fi Version Time is now: 10th January 2009 - 04:06 AM
hosted by : L M Photonics Ltd