we have one 55kw 3phase IM delta connected, which is run by DOL starter. Here are the mesured values
rated KW -55KW, O/P KW -1775KW, LOADING% - 42.3, EFF% - 88.5 WE ARE PLANNING TO GO FOR DELTA/STAR STARTER. IS THERE WILL BE ANY ENERGY SAVING? DEFINETLY YES. BUT HOW IT IS CACLCULATED ? |
|
|
|
Oct 3 2007, 06:50 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,086 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello CB TRIPATHI
Welcome to the forum You will not save energy by replacing a DOL starter with a star delta starter. The start current in star will be less than the start current in delta, but the machine will take longer to start. The total energy consumed will be about the same provided that the motor can get to full speed in star. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |