I need some design help. I am trying to help someone design in a contactor for use in a pre-charge resistor circuit, where the contactor will only close AFTER the pre-charge resistor has been in the circuit for 1.2 seconds. The question is, does the contactor still need a capacitive duty rating? I say yes, because when it opens it still has to contend with the extra arcing as the capacitors discharge. One of my cohorts says no, because the inrush has already been taken care of by the resistors, so the contactor is just acting to bypass the resistor and when opening, the arc will transfer back to flowing through the resistors. I have searched long and hard for information on selection criteria for pre-charge resistor contactors, but can't find anything useful. Anyone have an opinion or suggestion?


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
marke
post Oct 10 2007, 12:50 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Jraef

Provided that the capacitors are fully charged when the contactor is closed, it should not need to be capacitor rated for normal operation.
Opening is not an issue with capacitors unless there is significant inductance in the circuit.

The only issue is the abnormal operation such as voltage surges and transients. If the capacitors are line fed, then any disturbance on the supply will cause current transients and these can cause issues with the contactor if it is thermally rated.

I always used thermal rated contactors with a 30% overload capacity for the soft charge contactor on VSDs and never had any problems.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
jraef
post Oct 10 2007, 01:01 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 658
Joined: 22-February 03
From: USA, California
Member No.: 285



Excellent Mark, thanks.

I found an indirect reference indicating a 22% derate (which is what we apparently do with our PFC cap control contactors with built-in pre-charge resistors), so I think I'll go with your 30% to be sure.


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 ndoan 1,084 19th May 2003 - 06:26 AM
Last post by: GGOSS
No New Posts   1 dip04051978 898 16th August 2003 - 10:29 PM
Last post by: marke
No New Posts   9 foxhoundme 3,062 8th September 2005 - 12:33 PM
Last post by: PANKAJ
No New Posts   3 foxhoundme 882 30th April 2004 - 12:03 AM
Last post by: GGOSS
No New Posts   1 chaterpilar 607 25th December 2005 - 11:21 PM
Last post by: marke



RSS Lo-Fi Version Time is now: 10th January 2009 - 03:34 AM
hosted by : L M Photonics Ltd