Power Factor Capacitor Question
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
chisam14
post Nov 7 2007, 08:52 PM
Post #1


Junior Member
**

Group: Members
Posts: 4
Joined: 22-October 07
Member No.: 3,920



I have two single phase, 120V motors in parallel. One is a 3/4 hp(10.4A) and the other is a 1/4hp(4A). I need to know what size capacitor to put in parallel with them to help aid power factor. The cap will be controlled by a microprocessor. If anyone knows the size or formulas for calculating the size please let me know.
Go to the top of the page
 
+Quote Post
marke
post Nov 8 2007, 02:30 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



To determine the amount of correction to apply, you first need to determine the level of the magnetizing current.
If you run the motors open shaft, (No shaft load) then the current drawn will essentially be the magnetizing current.
If you apply static correction, then the correction current should be 80% of the magnetizing current.
If you apply bulk correction, then you can correct higher than that.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
AB2005
post Nov 8 2007, 07:25 AM
Post #3


Senior Member
*****

Group: Full Member
Posts: 223
Joined: 21-October 06
Member No.: 2,159



QUOTE(chisam14 @ Nov 8 2007, 01:52 AM) *
The cap will be controlled by a microprocessor.


Why you want to use microprocessor? According to your question, you want to connect capacitor at motor terminal (static correction) then there is no need of microprocessor. You calculate the capacitor as Marke replied.


--------------------
"Don't assume any thing, always check/ask and clear yourself".
Go to the top of the page
 
+Quote Post
marke
post Nov 13 2007, 07:14 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Once you determine the amount of reactive current that you need, you can calculate the impedance using ohms law.
Z = V/I
When you have calculated the impedance, you can calculate the capacitance as z = 1/(wc)
therefore C = 1/(2 x pi x F x Z)

or you can multiply the volts time the amps, divide by 1000 to get the required KVAR.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -Billy- 3,373 6th May 2002 - 10:22 PM
Last post by: marke
No New Posts   0 Asad 2,368 11th May 2002 - 03:24 AM
Last post by: Asad
No new   62 marke 19,385 27th December 2008 - 03:58 AM
Last post by: marke
No New Posts   2 Itos 2,372 13th August 2002 - 03:40 PM
Last post by: nadeem1990pk
No New Posts   4 Itos 2,128 24th June 2002 - 04:02 AM
Last post by: Itos



RSS Lo-Fi Version Time is now: 10th January 2009 - 01:47 AM
hosted by : L M Photonics Ltd