Dear Friends,
A 15kw motor driven hoist is connected through a VFD. The application being tough we had connected VFD of capacity 18.5kw and started using the hoist. It takes a load of 3 ton and beyond it does not hold the load. What is the reason for that. Some one says that it has to be used with Dynamic Breaking Unit and DB Resistor. Please explain. |
|
|
|
Nov 30 2007, 12:19 PM
Post
#2
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 31 Joined: 27-June 06 From: India, Vadodara Member No.: 1,583 |
In hoist application, regeneration takes place from the motor side while lifting. Therefore the DC voltage will increase till a limit and then the VFD will trip under DC bus overvoltage. In order to dissipate this excess energy, Brake Chopper and Resistor is required. You need to size the DBR as per your application requirement.
Regards, Anurag |
|
|
|
Dec 4 2007, 08:47 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 7 Joined: 4-October 07 Member No.: 3,864 |
Drive for hoist application
In hoist application, regeneration takes place from the motor side while lifting. Therefore the DC voltage will increase till a limit and then the VFD will trip under DC bus overvoltage. In order to dissipate this excess energy, Brake Chopper and Resistor is required. You need to size the DBR as per your application requirement. Regards, Anurag |
|
|
|
Dec 4 2007, 09:01 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Ramasubramanian
Can you give us more detail on the problem that you are having. QUOTE beyond it does not hold the load Do you mean that it will not hold the load stationary, or that it will not lift the load, or it will not lower the load in a controlled fashion? There are a number of scenarios and if you can give us more detail, it will be easier to give you a meaningful answer. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | marke | 1,156 | 13th May 2002 - 09:37 AM Last post by: marke |
|||
![]() |
0 | weiwei2 | 3,863 | 1st October 2002 - 02:37 PM Last post by: weiwei2 |
|||
![]() |
4 | GGOSS | 1,268 | 14th December 2008 - 06:08 PM Last post by: marke |
|||
![]() |
2 | DDoerschuk | 1,201 | 6th February 2003 - 04:44 AM Last post by: DDoerschuk |
|||
![]() |
0 | markfoley | 1,093 | 26th February 2003 - 12:36 PM Last post by: markfoley |
|||
|
Lo-Fi Version | Time is now: 10th January 2009 - 01:58 AM |