Harmonics And Vfds
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
marke
post Dec 31 2007, 02:36 AM
Post #1


Posting Freak
******

Group: Moderator
Posts: 2,054
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



One of the areas that I operate in, has a high density of VFDs on pumps on relatively weak supplies. The result is that the high levels of harmonics on the VFD inputs has accumulate in the supply and is causing a high THD of the supply voltage. While we do have supply regulations covering harmonics, in this instance, the harmonics are higher than they should be.

There is an option of using zig zag transformers and six phase rectifiers as a means of reducing the harmonics drawn by drives however in this case, the drives are already installed.

There is a transformer for each drive and sizes range up to 200KW.

One thought that I had, was that for future installations, and there are new installations going in all the time, that the new supply transformers be designed with a zig or a zag winding to give a phase shift, and install equal loading on the leading and lagging phase shifts. This should act like a twelve pulse input on one drive, only it will be across two drives.

Any thoughts on this??

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
mariomaggi
post Jan 1 2008, 10:47 AM
Post #2


Member
****

Group: Full Member
Posts: 198
Joined: 15-March 05
From: Milan, Italy
Member No.: 1,068



Dear Marke,
happy new year - first of all.

Your solution is valid if both drives are energized together, otherwise you will lose the benefit.
If local rules are not so stringent, it is possible to use this solution, accepting to have more harmonics when one load is disconnected.

Regards
Mario


--------------------
Go to the top of the page
 
+Quote Post
marke
post Jan 1 2008, 07:02 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,054
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Mario

Compliments of the season to you also.

This region has around 2000 VFDs installed at present and the harmonics are high. New VFDs are going in daily, so my though was to recommend phase shift transformers for all new installations and this would over time help to reduce harmonic levels, which is probably a better solution that installing future drives with filters etc and leave existing harmonics in place.

Drives are for controlling irrigation pumps and there is one transformer per pump, so it is practical to do and all drives tend to run at the same time.

Have a good day,
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
anu_rags
post Jan 2 2008, 01:50 PM
Post #4


Intermediate Member
***

Group: Full Member
Posts: 29
Joined: 27-June 06
From: India, Vadodara
Member No.: 1,583



Hi Mark,

At one such place, we were required to provide drives that meet IEEE519 standards for current and voltage. We had 4 no drives of equal size. A 12 pulse drive wont have been able to match the harmonics standards. We were looking for a phase shifting transformer for quase 24 pulse system with 6pulse drives. I was not able to find any suitable manufacturer of such transformers. Have you come across any such trafo?

Regards,
Anurag
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   8 marke 6,222 3rd November 2006 - 01:00 PM
Last post by: Tim
No New Posts   9 marke 1,628 3rd July 2002 - 10:39 AM
Last post by: marke
No New Posts   1 Lewis 1,213 4th October 2002 - 09:11 PM
Last post by: marke
No new   14 GGOSS 1,489 28th January 2003 - 04:08 PM
Last post by: gwosun
No New Posts   0 GGOSS 1,603 10th September 2002 - 08:11 AM
Last post by: GGOSS



RSS Lo-Fi Version Time is now: 22nd August 2008 - 12:37 AM
hosted by : L M Photonics Ltd