AC Drives are sold with voltage ratings and HP ratings ,
now, my question is will a 40 hp 460 volts 60hz variable speed drive be suitable to be used in a place having 380volts 60 hz power supply to drive a 40 hp/380 volts motor. I feel drive has to be derated by 17%. Any thoughts.. |
|
|
|
Jan 15 2008, 06:08 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello chaterpilar
There are two issues here. 1. Will the drive operate on 380 volt? and 2. what will the rating be. 1. Most modern drives operate all the electronics from a switch mode supply off the DC bus so there should bee no problem operating the electronics off the lower voltage except that the under voltage and over voltage trip settings will need to be altered. You would need to talk to the supplier about doing that. 2. The real rating of the drive is not power, it is current. When you reduce the supply voltage, the current will stay the same, so the power rating will drop by the same amount as the current. If you are looking for a unit to operate on 380 volt 60Hz, you could use any drive designed for the European market. The 50 Hz or 60Hz on the input will make no difference to the operation of the drive. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jan 16 2008, 03:28 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 5 Joined: 11-January 08 Member No.: 4,182 |
See the operating voltage range of drive.If it is within your requirement,you can run drive at different voltage.
Otherwise it is not advisable to operate the drive beyond the specified voltage range. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
5 | magdy El Kady | 1,548 | 26th September 2002 - 10:10 AM Last post by: GGOSS |
|||
![]() |
3 | jackson8000 | 1,242 | 20th January 2003 - 09:12 AM Last post by: marke |
|||
![]() |
1 | dip04051978 | 898 | 16th August 2003 - 10:29 PM Last post by: marke |
|||
![]() |
4 | noble | 1,377 | 2nd November 2004 - 07:55 AM Last post by: RalphChristie |
|||
![]() |
3 | Otto | 1,418 | 2nd February 2004 - 07:30 AM Last post by: jraef |
|||
|
Lo-Fi Version | Time is now: 10th January 2009 - 02:34 AM |