Input Protection Scheme For Msf
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
gaurav1981
post Feb 20 2008, 01:06 PM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 11
Joined: 3-August 07
Member No.: 3,568



Dear All,

MSF manual suggests on using normal fuses for short circuit protection of MSF.

There is no ground fault protection in MSF.

Question is , whether we can use MCCB , 3 pole with adjustable O/L, S.Ckt & ground fault protection or as O/L protection will be provided by MSF itself, wecan use normal HRC fuses along with ground fault relay/ monitoring relay.

What i know is that the earthing scheme used in the installation effects the choice of ground fault relay.

Except this what other protection is ideally required at the input of MSF for trouble free operation, as i recently faced a major failure & even the customer was not forthcoming on the events prior/during the fault.

Thanks & Regards,
Gaurav

Go to the top of the page
 
+Quote Post
marke
post Feb 20 2008, 06:10 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Gaurav

It really depends on what you want to protect, and what conditions you want to protect against.

If you wish to protect the SCRs against an overcurrent situation (abnormal current such as a short circuit) then the best protection is offered by semiconductor fuses.
Bypass contactors also offer much higher security against a problem while the starter is running, but not during start.

Over voltage problems are usually an issue when the starter is OFF but has voltage applied. Under this case, the SCRs are blocking the full voltage and are subjected to transients which can damage the SCRs. The best protection against the transients is to use a line contactor which is opened when the starter is not running. Use the starter to control the contactor.

Standard HRC fuses are primarily to protect the cables used and should be sized accordingly. They are too slow to provide short circuit protection for the SCRs.
A circuit breaker can be even slower than the HRC fuses and allows more fault current through so provides a lower protection to the SCRs under short circuit conditions.

Apply earth fault and cable protection as you would without the soft starter. Then consider the addition of semiconductor fuses, line contactor and bypass contactor for added protection of the soft starter against major faults.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   9 marke 1,769 3rd July 2002 - 10:39 AM
Last post by: marke
No New Posts   0 marke 2,855 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 -mahesh- 1,754 4th April 2006 - 06:08 AM
Last post by: khongai
No New Posts   3 tahira 3,073 22nd August 2003 - 09:01 AM
Last post by: sethar
No New Posts   0 tahira 706 --
Last post by: tahira



RSS Lo-Fi Version Time is now: 10th January 2009 - 01:53 AM
hosted by : L M Photonics Ltd