Static Power Factor Capacitor, Connection Scheme
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
dennis3834
post Feb 20 2008, 07:46 PM
Post #1


Junior Member
**

Group: Full Member
Posts: 6
Joined: 20-February 08
Member No.: 4,312



Dear All,

This is my first post in the forum.

I have a motor for a blower fan, at running conditon the load current will be constant. Our system has a bulk power factor capacitor controlled by a power factor controller with 6 steps set to maintain an overall power factor of 95%. The location of the motor under consideration is quite far from the bulk power factor correction. I want to add a static power factor capacitor to my motor taking consideration the standard installation of capacitor correction. I want to correct my PF on the motor to 0.95PF. I will set the static Power Factor capacitor to engage faster than the bulk capacitor, is my idea acceptable.. please advice...

Thanks
Go to the top of the page
 
+Quote Post
marke
post Feb 20 2008, 07:59 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello dennis3834

Yes, you can apply static correction to the motor. This will reduce current in the cable supplying the motor and may save a few watts for you.
If you are using static correction, you should limit the correction to 80% of the magnetizing current of the motor. This may or may not take the motor to 0.95pf. You must be careful not to correct too much as you can cause resonance problems. You are best to use a separate contactor to control the capacitors and use the starter controls to control this contactor.
If you are using a soft starter, use the bypass control to control the capacitor contactor so that the capacitors are connected once the voltage reaches full voltage.DO NOT connect the capacitors to the output of the soft starter!

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
dennis3834
post Feb 21 2008, 04:28 AM
Post #3


Junior Member
**

Group: Full Member
Posts: 6
Joined: 20-February 08
Member No.: 4,312



Marke,

Thanks for the early response. Just to clarify, what will happen if i set the correction to 80% of the magnetising current of the motor and my bulk capacitor is set to cater a 95% power factor of the system, when both the static capacitor and the bulk correction capacitor is connected, do the power factor of the motor get affected by the bulk capacitor??
Go to the top of the page
 
+Quote Post
marke
post Feb 21 2008, 06:03 PM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Dennis

The power factor of the motor does not actually change at all, it is the power factor as seen from the supply which is the combination of motor and capacitors.

If you apply static correction to the motor, you will reduce the amount of bulk correction required.
If the bulk correction is automatic, it will adjust to keep the power factor within limits.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
dennis3834
post Feb 21 2008, 07:14 PM
Post #5


Junior Member
**

Group: Full Member
Posts: 6
Joined: 20-February 08
Member No.: 4,312



Mark,

thanks for the enlightment
Go to the top of the page
 
+Quote Post
dennis3834
post Feb 27 2008, 04:34 PM
Post #6


Junior Member
**

Group: Full Member
Posts: 6
Joined: 20-February 08
Member No.: 4,312



Can you provide me the equation how to compute the capacitor required when the magnetizing current is 100amp and motor voltage is 400volts, 3 phase. Lets assume that the capacitive current would be 80% of the magnetizing current..
Go to the top of the page
 
+Quote Post
marke
post May 11 2008, 02:54 AM
Post #7


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Have a look at Power Factor Calculations

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -Billy- 3,373 6th May 2002 - 10:22 PM
Last post by: marke
No New Posts   0 Asad 2,368 11th May 2002 - 03:24 AM
Last post by: Asad
No new   62 marke 19,385 27th December 2008 - 03:58 AM
Last post by: marke
No New Posts   1 Itos 1,270 18th June 2002 - 04:56 AM
Last post by: marke
No New Posts   2 Itos 2,372 13th August 2002 - 03:40 PM
Last post by: nadeem1990pk



RSS Lo-Fi Version Time is now: 10th January 2009 - 02:03 AM
hosted by : L M Photonics Ltd