Welding Set
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
anu_rags
post May 17 2008, 10:36 AM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 29
Joined: 27-June 06
From: India, Vadodara
Member No.: 1,583



Dear All,

I have an application Welding Set, on which I have to install a VFD. Welding Set is 200kva 415V, 2 phase input. Power Supply is from Generator which has a 3 phase output. Presently without a VFD, the Welding Set creates unbalance load at the Generator. I think that if VFD is installed in between, the problem of unbalance load can be solved. My worry is that since only 2 phase output of VFD will be used, will the VFD trip on motor cable open at output?

Has anyone installed a VFD in such application?

Regards,
Anurag
Go to the top of the page
 
+Quote Post
marke
post May 17 2008, 08:51 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,063
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi

My answer would be No, I have not done this and I do not think that it will work.

A VFD is designed for a three phase load and connecting a sigle phase load across two phases will not yeild the correct waveform and current in the load, plus I would expect that the inverter protection would not be happy.
You would probably be better looking at some form of UPS which is designed for this type of operation.

As a thought, if you are concerned about the loading on the generator, why not look at a transformer with a delta primary and a star secondary on the output of the generator. This would help to even up the load a little.

Best regards,
Mark


--------------------
Go to the top of the page
 
+Quote Post
VST
post May 19 2008, 03:24 AM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 11
Joined: 9-May 08
Member No.: 4,545



Dear Anu_Rag,

As marke said I feel same thing. No VFD will support such application. A very basic version of inverter(unlike Vector control etc) may work .

But then too, whenever your transformer does welding work, your dc link will be dipped. And very next instance when the welding is off there will be over voltage on the Bus. So the capacitor will be under heavy charge discharge cycle. And very soon they will bust.

May be the IGBT support for this.

I think this may work with current source inverter.

In one of the Ac drive (Mostly Simovert P or A from siemens) I have seen drive works even one arm is disconnected at the output.

But balancing the the impedence is certainly not possible.

Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   6 ram14375 752 30th March 2007 - 08:48 AM
Last post by: ram14375
No New Posts   0 DEEPAK MATHUR 285 24th May 2008 - 03:55 PM
Last post by: DEEPAK MATHUR



RSS Lo-Fi Version Time is now: 8th September 2008 - 01:18 AM
hosted by : L M Photonics Ltd