Overload Realy Setting |
![]() ![]() |
Overload Realy Setting |
May 18 2008, 01:01 PM
Post
#1
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 57 Joined: 17-December 05 Member No.: 1,308 |
hello everybody
if we install capacitor across motor we have to make necessary adjusments in the overload relay have we to adjust overlaod relay setting if we provide the same capcitor before overload relay and contactor(in the same starter -dol.ie after isolator) ram |
|
|
|
May 18 2008, 07:20 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello ram
Ideally, you should connect the capacitor before the overload relay so that the overload relay sees all the current going into the motor. If you connect the capacitance after the overload relay, you will need to make adjustments to it's settings and you will be more prone to overload trips due to harmonic bursts into the capacitor etc. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
6 | gogo | 1,133 | 11th January 2003 - 08:55 PM Last post by: TheOne |
|||
![]() |
1 | Les L | 1,275 | 8th December 2004 - 08:04 AM Last post by: -Anonymous- |
|||
![]() |
13 | GGOSS | 3,921 | 20th November 2003 - 02:21 AM Last post by: jraef |
|||
![]() |
1 | merajdab | 1,033 | 16th August 2003 - 10:19 PM Last post by: marke |
|||
![]() |
1 | normannicklette | 1,917 | 1st November 2004 - 08:01 AM Last post by: RalphChristie |
|||
|
Lo-Fi Version | Time is now: 2nd December 2008 - 11:01 PM |