I want to know that what is the diffrence between Variable Speed Drives and Soft Starters ? Define basic diffrence in short please ?
|
|
|
|
Aug 24 2003, 05:05 AM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 27-December 02 Member No.: 218 |
Hi Sethar
The simplest explaination would be that a VSD is device for varying the speed of a drive either at startup, during operation or during shutdown, while a soft starter is a simpler device(similar to a VSD as far as controlling the voltage and frequency of supply) but is normally used during startup. |
|
|
|
Aug 24 2003, 05:16 AM
Post
#3
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,060 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Sethar
A soft starter comprises one or more SCR pairs connected in series with the supply to the motor. These SCRs are used to reduce the voltage applied to the motor during start. The reduced voltage results in a reduced starting current and torque. A variable speed drive is an inverter that rectifies the incoming supply, generating a high voltage DC. This DC is then chopped up converting the DC back into AC of variable voltage and frequency. The speed of the motor is altered by altering the frequency applied to it. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Sep 5 2003, 10:07 PM
Post
#4
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 643 Joined: 22-February 03 From: USA, California Member No.: 285 |
Just to correct a slight mistake in the first response, a Soft Starter cannot change the output frequency, only the voltage. For that reason, a Soft Start cannot be used to change motor speed. It simply ramps the motor up (or down) but only operates continuously at full speed.
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Sep 24 2003, 02:15 AM
Post
#5
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 404 Joined: 17-May 02 From: Melbourne Member No.: 14 |
Hello Sethar,
In very simplistic terms, the function of each is as follows; A soft starter is used to accelerate a motor/load from zero speed to rated speed over a user adjustable period of time. The process is achieved by controlling the voltage applied to the motor terminals during starting. A variable frequency drive enables the user to control the speed of the motor/load. The process is achieved by varying both the voltage and frequency (Hz) of the supply to the motor. Regards, GGOSS |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
32 | marke | 12,931 | 28th March 2008 - 01:02 PM Last post by: lau |
|||
![]() |
5 | uhaykir | 2,101 | 5th July 2002 - 09:08 AM Last post by: marke |
|||
![]() |
3 | marke | 2,217 | 24th January 2003 - 07:05 PM Last post by: marke |
|||
![]() |
1 | marke | 2,178 | 14th July 2003 - 12:44 AM Last post by: GGOSS |
|||
![]() |
3 | -Ravisankar- | 1,792 | 28th June 2002 - 08:04 AM Last post by: GGOSS |
|||
|
Lo-Fi Version | Time is now: 29th August 2008 - 04:45 AM |