IPB

Welcome Guest ( Log In | Register )

Quick Register
Welcome Guest, Register to Remove this Message!
Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now

There are many great features that are not available to guests at LMPForum
Login User Name

Login Password



Forgot Password

Profile
Personal Photo
Rating
 
Options
Options
Personal Statement
msayed doesn't have a personal statement currently.
Personal Info
msayed
Junior Member
Age Unknown
Gender Not Set
Location Unknown
Birthday Unknown
Interests
No Information
Statistics
Joined: 9-January 10
Profile Views: 100*
Last Seen: 1st February 2010 - 01:05 PM
Local Time: Sep 10 2010, 02:52 PM
3 posts (0.01 per day)
Contact Information
AIM No Information
Yahoo No Information
ICQ No Information
MSN No Information
Contact Private
* Profile views updated each hour

msayed

Members

**


Topics
Posts
Blog
Comments
Friends
My Content
9 Jan 2010




I'd like to thank all founders of this forum because it's really very useful.

I have a motor drived by a soft starter and I want to make sure that the motor is suitable for the application. Kindly consider the following specifications for the motor, fan, soft starter.



1- Specifications of the fan are:



Induced fan,

Type: Y5- 48N016.5D

Volume: 85000 m3/ h

Full pressure: 2000 Pa

Fan rotational speed: 960 r.p.m

Motor power: 75 KW

Medium temperature: 270 ºC

Medium <A name=OLE_LINK1>titer: 0.648 Kg/ m3



2- Specifications of the motor are:



Type: 315S-6

Power: 75 KW

Voltage: 380 V

Current: 142.4 A

Frequency: 50 HZ

Efficiency: 92.8

Speed: 990 r.p.m

Insulation class: B

Tst / TN : 1.6

Ist / In : 6.5

Tmax / Tn : 2



3- Specifications of the soft starter are:



Power: 132 KW

Current: 250 A





We tried to start the motor by the soft starter many times by different parameters setting but each time the soft starter trips during the starting period and generate alarm (thermal motor model overload), some of the settings used were:





1- Rated current: 142 A,

Starting mode: voltage ramp+ current limit,

Starting voltage: 40%,

Starting time: 30 sec.

Current limit: 400 %

Tripping class: 10



2- Rated current: 142 A,

Starting mode: voltage ramp+ current limit,

Starting voltage: 40%,

Starting time: 25 sec.

Current limit: 450 %

Tripping class: 20



3- Rated current: 142 A,

Starting mode: voltage ramp+ current limit,

Starting voltage: 40%,

Starting time: 30 sec.

Current limit: 500 %

Tripping class: 20



The motor started only after changing the tripping class parameter to trip class 30 and the motor run successfully and drew a current of 80 A. the starting time has also to be parameterized to at least 30 sec. to start the motor.



Now we adjusted the soft starter for the following parameters:

Rated current: 142 A,

Starting mode: voltage ramp+ current limit,

Starting voltage: 40%,

Starting time: 30 sec.

Current limit: 450 %

Tripping class: 30





We are interested in the starting time and tripping class 30, Are these settings suitable for the motor or it is required to replace the motor by another one can withstand this heavy starting load.