p.f calculation for transformer |
![]() ![]() |
p.f calculation for transformer |
Oct 14 2002, 11:23 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 11 Joined: 29-August 02 Member No.: 70 |
We have system of two single-phase transformers in one unit (Varivolt system) i.e. secondary of transformer T1 is connected to the primary of second transformer T2. By varying the secondary of T1 we get variation in primary and secondary of T2.The specification of transformers:
T1: 1 phase 1302KVA, 50HZ, primary 11kv, 118A, secondary 330-1210v, 1207A with Z%= 11 T2: 1 phase 1500KVA, 50HZ, primary 1119kv, 1250A, secondary 2*93.3 v, 2*7500A with Z%= 6 B/w two connection i.e. secondary of T1 and Primary of T2 we have 3 individual cap banks, each rating is Qn = 300KVAr, Un= 1200V, Cn=663microF, Ic = 250A, Hz = 50 The load at secondary of T2 is an arc furnace with max load of 850KW. As I know through the seimens hand book that the cap rating for transform is near to the 80-90% of the reactive full load power of the transform. With formula Qtr = Q0 + Uz/100% (S/Sn) ^2 * S Where Qtr = transformer reactive power, Q0 is the transformer no load power, S = apparent power that a transformer is supplied, Sn = rated power for transformer, Uz is the % impedance of transformer. Here in our case Q0 from seimens graph = 27 Kvar S= 1302 for full load Thus Qtr = 27 + 11/100 (1302/1302)^2 * 1302 = 170KVAR Which is not fulfill in our case, can you suggest me what is the exact relation to calculate the cap bank KVAr and step required to control the p.f in case of transformer, is the bank rating equal to kva rating of transformer? Is there any effect on the secondary voltage of the transform if the cap bank is over rated i.e. if load on transform is reduced? |
|
|
|
Oct 16 2002, 09:24 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello tahira
A transformer has two components of current flowing, one is the resistive current and the other is the inductive or reactive current. On a single transformer, the reactive, or magnetising current is constant and independant of load. There is an additional reactive component due to the leakage reactance of the transformer, and this does vary with the load. Unlike an induction motor, the dangers associated with over correction are essentially eliminated due to the fact that the transformer does not act as a generator. You can however, get an elevated voltage due to correction but this is not major. With a transformer, I would suggest that you measure the current with the secondary open circuit. This current is essentially magnetisng current and can be fully corrected. As the load is increased, the reactive component will also increase and the power factor will begin to lag. You could add more correction when the load is high, but it depends on how accurate you actually need to be. Automatic correction is probably the best solution for your application, because you are varying the reactive current in the second transformer by varying the voltage. Your load of an arc furnace will probably have a very poor power factor, not just due to the reactive current, but also due to the distortion of the current waveform. This distortion can not be reduced by the use of power factor correction, so you may still have a poor power factor and high KVA demand. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Oct 24 2002, 01:17 PM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 11 Joined: 29-August 02 Member No.: 70 |
hi Mark
thanks for nice explaination regarding the subject matter .. still plz tell me , is there any calulation for cap bank for transformer , how can we select the cap bank for transformer regards tahira |
|
|
|
| Guest__* |
May 21 2004, 06:28 AM
Post
#4
|
|
Guests |
hi mark
I am your new friend can you help me about transformer |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
11 | Alnerthyrn | 2,226 | 29th March 2005 - 02:44 AM Last post by: jraef |
|||
![]() |
1 | Roomsk10 | 1,358 | 19th March 2003 - 09:59 AM Last post by: marke |
|||
![]() |
5 | noble | 1,613 | 9th June 2003 - 11:16 AM Last post by: marke |
|||
![]() |
2 | ALTAF | 6,541 | 1st November 2004 - 07:39 AM Last post by: RalphChristie |
|||
![]() |
0 | islah | 656 | 16th February 2004 - 07:44 AM Last post by: islah |
|||
|
Lo-Fi Version | Time is now: 2nd December 2008 - 11:20 PM |