Hi gents!
We are recently working on a substation having 132/11kV system with 36MVA transformer (Y-Y with treasery winding). There are differential, O/C, U/V, O/V, E/F and all other transformer protections is there with individual protection for different feeders (S/C, E/F, O/C). I have following quires: 1. What is the difference b/w unrestricted and restricted earth fault protection, how they differ and what are there selecting criteria according to application, which one provided more accurate and complete protection? 2. What is the setting procedure for differential protection? 3. Selection criteria of protection relays setting i.e. O/V, U/V, O/C and S/C. 4. What is directional O/C relay, how they differ from no directional relay, is there any advantage for using directional relay? 5. Plz info me any web site given me details about protection relays (cables feeder protection, …)? 6. Is any one having info about E-Tap software? Best regards ASD |
|
|
|
Jan 19 2003, 06:53 PM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 18-January 03 Member No.: 246 |
Hello tahira,
Regarding item #6, ETAP software is very good. We use it exclusively for analysis, coordination, etc. You can find it at www.etap.com. Good luck. |
|
|
|
Mar 21 2003, 01:09 PM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 30 Joined: 8-November 02 From: Northern Cape, South Africa Member No.: 168 |
I would suggest that you visit following sites
http://www.geindustrial.com/pm/notes/artsci/ - go to transformer protection http://www.selinc.com/techpprs.htm http://www.ee.polyu.edu.hk/staff/eekkli/BE.../Ch3_OC2003.pdf - very good - about relaying http://www.usace.army.mil/inet/usace-docs/...ytm/tm5-811-14/ http://www.relaylounge.com/servlet/Content...id=987664718399 For last one you have to register (free) - then go to NPAG relay technology It is a lot of places - but there is good information Good luck RCC |
|
|
|
Aug 22 2003, 09:01 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 8 Joined: 31-July 03 From: karachi Member No.: 438 |
Hello tahira,
1. Unrestricted earth fault is used for feeder protection,not for limited zone & less sensitive. Restricted earth fault is used for transformer protection ,it is also called ground diffrential & limited to zone , not will trip beyond the zone. Restricted is more accurate protection. 2. Setting procedure of diffrential depends on both side Pri/Sec current & CT ratio ( Suppose in case of transformer Delta to Star) Star side I = 1600 A & CT is 2000/1 Delta side I = 52 A & CT is 75/1 1600/2000=base current 52/75=base current those settings intered into relay includind system parameters actually diffrential relay sense ratio/deffrence between both side in term of % according to settings + error in base current ratio, in this relay no any time setting is required it take action on immediate effect as sense diffrence. 3. Selection criteria of protection relays depends system designe/load/criticality /as per current carrying capacity of equipment/short ckt values/i.e down stream side settings should be lower than up stream side. 4. Directional relay is better than withour directional relay it woks/sense through one direction only. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | marke | 2,656 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
4 | GGOSS | 939 | 5th September 2002 - 07:45 AM Last post by: GGOSS |
|||
![]() |
1 | -mahesh- | 1,666 | 4th April 2006 - 06:08 AM Last post by: khongai |
|||
![]() |
0 | tahira | 665 | -- Last post by: tahira |
|||
![]() |
1 | normannicklette | 1,917 | 1st November 2004 - 08:01 AM Last post by: RalphChristie |
|||
|
Lo-Fi Version | Time is now: 2nd December 2008 - 11:03 PM |