IPB

Welcome Guest ( Log In | Register )

Quick Register
Welcome Guest, Register to Remove this Message!
Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now

There are many great features that are not available to guests at LMPForum
Login User Name

Login Password



Forgot Password

Profile
Personal Photo
Rating
 
Options
Options
Personal Statement
rvim002 doesn't have a personal statement currently.
Personal Info
rvim002
Intermediate Member
Age Unknown
Gender Not Set
Location Unknown
Birthday Unknown
Interests
No Information
Statistics
Joined: 3-April 08
Profile Views: 397*
Last Seen: 12th June 2009 - 03:32 AM
Local Time: Mar 15 2010, 12:07 PM
12 posts (0.02 per day)
Contact Information
AIM No Information
Yahoo No Information
ICQ No Information
MSN No Information
Contact Private
* Profile views updated each hour

rvim002

Full Member

***


Topics
Posts
Blog
Comments
Friends
My Content
16 Feb 2009
Hi All

We are thinking of putting in a regen DC Drive to a crane for hoisting, travel motions.

The supply is from crane collector rails and sometimes, there might be small glitches and blips in power supply since the power supply rails are old and not necessarily flat.

I think that since DC Drives do not have any energy storage elements ( Like the DC Capacitors in the AC Drives), momentarily power sag might trip the drive very often and will cause nuisance. So I'm pushing towards replacing the DC motor with AC Motors and AC Drives.

Am I right in my assumption?
15 Jan 2009
Hi all,

I have been going through a couple of VSD Manuals and I've noticed the following.

For EMC Requirements, VSD manufacturer advises to use Shielded cables

But when using shielded cables, the max length of the cable is reduced when comparing with the unshielded cable.

I thought it is contradictory. Say, the motor is 100m from the VSD. If I use shielded cable, condition 1 is satisfied, but for condition 2, I can only use a maximum of 50m of shielded cable, whereas I can go upto 100m if its unshielded.

I guess
1. Shielded VSD cables help reducing radiated noises and reduce interference (by returning the noise back to VSD and not radiating) and helps in complying with EMC requirements .

2. At the same time, by using shielded cables, the spikes are reflected back to the VSD itself. But, if an unshielded cable is used, the noises don't return to the VSD, but are radiated. So, by choosing to use a shielded cable at the output of the VSD, we are degrading the performance of the VSD because of the reflected noise. Hence the length of the cable is reduced when shielded cables are used.

So, after a particular length is exceeded, to meet the EMC requirements, one has to use a shielded cable AND output chokes.

Is my understanding correct?

Please advise

Cheers
12 May 2008
Hi,

I am looking at a spec sheet of a motor which has a starting torque of 140% and a breakdown torque of 241%.

Now, if the load that is attached to the motor is small ( say 50% at the rated speed and even less than that at speeds below it..), does the motor still produce 241% of breakdown torque. ie, as the motor accelerates from 0 speed to rated speed, at the speed at which breakdown torque occurs in the torque speed curve, does the motor practically produce the 241% torque inspite of the motor load being small?

Thanks in advance...
6 Apr 2008
Hi All,

The quality of the content I get from this forum is just fantastic. Thanks for all the info.

I am in a process of specifying the transformer capacity for starting three 1250HP motors. I looked into a few websites for the transformer sizing guidelines and this is what I have come up with.

I assume that it is going to be a 5.7% impedance transformer. I would require the two motors running and the third motor to be started, with a maximum of 10 % voltage drop at the motor terminals.

Motor nameplate details:
1250 HP
3300V
Locked rotor current: 1254 A
Full load current: 198 A
Full load power factor: 86%
Code Letter: G


Calculation of motor starting kVA:

For Code G motor, starting kVA = 6.29 times Horsepower

So,

Motor starting kVA = 6.29 x 1250
= 7.862 MVA

Transformer sizing:

Total transformer kVA size required = ( Running kVA rating of two 1250 HP motors) + ( Transformer rating required to start the 3rd motor with 10 % Volt drop)

Running kVA Rating of 1250 HP motors = 1.732 * ( Rated Voltage) * ( Rated FL Current) / Assumed average power factor of 85%
=1.732 * 3300 * 198 / 0.85
= 1332 kVA
So, Running kVA of two 1250 HP Motors = 2 * 1332 kVA
= 2.664 MVA

Generally, Volt drop due to motor starting in % = Motor starting kVA / ( Motor starting kVA + Transformer short circuit kVA)

So, 10% = (7.862MVA) / ( 7.862 MVA + Transformer short circuit capacity)
So, calcualted transformer short circuit capacity = 70.76 MVA

Transformer Short circuit capacity = Transformer kVA rating / (Transformer impedance)
So, transformer kVA Rating = Transformer short circuit capacity * Transformer impedance
So, the transformer rating required to start the third motor with 10 % volt drop = 70.76 MVA * .057
transformer rating required to start the third motor with 10 % volt drop = 4.033 MVA

Recollect
Total transformer kVA size required = ( Running kVA rating of two 1250 HP motors) + ( Transformer rating required to start the 3rd motor with 10 % Volt drop)
= 2.664 MVA + 4.033 MVA
= 6.697 MVA

Does this approach seem right? Or am I going wrong somewhere?

I would actually be using softstarters in this case, but I need to prove that 5MVA transformer is not sufficient for DOL starting of third 1250 HP motor, with two other 1250 HP motors running.

Thanks in advance

Cheers




6 Apr 2008
Hi All,

I have got a question regarding the practical and theoretical speed-torque curve.

I have a motor datasheet which lists all the resistances, reactances of the equicalent circuit. I also have the speed torque curve for the motor. But when I use the values and calculate the speed torque curve from the equation, the curve is not having the similar values/shape as the curve they have provided. Is this because of the dynamic nature of the motor?

Is it possible to plot the speed torque curve from the motor parameters( R1, R2, Rm, X1, X2, Xm etc)? Will this plot be the same as what is plotted from the experimental values?