[edit] Star Delta Starter[edit] TechnologyStar/Delta starters are probably the most common reduced voltage starters in the 50Hz world. (Known as Wye/Delta starters in the 60Hz world). They are used in an attempt to reduce the start current applied to the motor during start as a means of reducing the disturbances and interference on the electrical supply. In many, if not most, cases the star/delta starter does little to reduce problems, infact it commonly exacerbates them. Tradditionally in many supply regions, there has been a requirement to fit a reduced voltage starter on all motors greater than 5HP (4KW). This regulation was introduced in order to reduce the start current, but unfortunately, a solution was specified rather than a result. The Star/Delta (or Wye/Delta) starter is one of the lowest cost electromechanical reduced voltage starters that can be applied and this is why it has been so popular. The Star/Delta starter complied with the regulations, but did not achieve the desired results. The Star/Delta starter is manufactured from three contactors, a timer and a thermal overload. The contactors are smaller than the single contactor used in a Direct On Line starter as they are controlling winding currents only. The currents through the winding are 1/root 3 (58%) of the current in the line. There are two contactors that are close during run, often referred to as the main contactor and the delta contactor. These are AC3 rated at 58% of the current rating of the motor. The third contactor is the star contactor and that only carries star current while the motor is connected in star. The current in star is one third of the current in delta, so this contactor can be AC3 rated at one third of the motor rating. [edit] OperationIn operation, the Main Contactor (KM3) and the Star Contactor (KM1) are closed initially, and then after a period of time, the star contactor is opened, and then the delta contactor (KM2) is closed. The control of the contactors is by the timer (K1T) built into the starter. The Star and Delta are electrically interlocked and preferably mechanically interlocked as well. In effect, there are four states:
This type of operation is called open transition switching because there is an open state between the star state and the delta state. [edit] Open Transition StartersWhen a motor is driven by the supply, either at full speed or at part speed, there is a rotating magnetic field in the stator. This field is rotating at line frequency. The flux from the stator field induces a curent in the rotor and this in turn results in a rotor magnetic field. When the motor is disconnected from the supply (open transition) there is a spinning rotor within the stator and the rotor has a magnetic field. Due to the low impedance of the rotor circuit, the time constant is quite long and the action of the spinning rotor field within the stator is that of a generator which generates voltage at a frequency determined by the speed of the rotor. When the motor is reconnected to the supply, it is reclosing onto an unsynchronised generator and this results in a very high current and torque transient. The magnitude of the transient is dependent on the phase relationship between the generated voltage and the line voltage at the point of closure, but typically can be much higher then DOL current and torque and can result in electrical and mechanical damage. [edit] Closed Transition Star/Delta StarterThere is a technique to reduce the magnitude of the switching transients. This requires the use of a fourth contactor and a set of three resistors. The resistors must be sized such that considerable current is able to flow in the motor windings while they are in circuit. The auxiliary contactor and resistors are connected across the delta contactor. In operation, just before the star contactor opens, the auxiliary contactor closes resulting in current flow via the resistors into the star connection. Once the star contactor opens, current is able to flow round through the motor windings to the supply via the resistors. These resistors are then shorted by the delta contactor. If the resistance of the resistors is too high, they will not swamp the voltage generated by the motor and will serve no purpose. In effect, there are five states:
[edit] Internal LinksElectric Motors [edit] External Links
|
| This page was last modified 22:16, 20 October 2007. This page has been accessed 218 times. Content is available under GNU Free Documentation License 1.2. Privacy policy About LMPWiki Disclaimers |