p.f calculation for transformer


tahira

Recommended Posts

We have system of two single-phase transformers in one unit (Varivolt system) i.e. secondary of transformer T1 is connected to the primary of second transformer T2. By varying the secondary of T1 we get variation in primary and secondary of T2.The specification of transformers:

 

T1: 1 phase 1302KVA, 50HZ, primary 11kv, 118A, secondary 330-1210v, 1207A with Z%= 11

T2: 1 phase 1500KVA, 50HZ, primary 1119kv, 1250A, secondary 2*93.3 v, 2*7500A with Z%= 6

 

B/w two connection i.e. secondary of T1 and Primary of T2 we have 3 individual cap banks, each rating is

 

Qn = 300KVAr, Un= 1200V, Cn=663microF, Ic = 250A, Hz = 50

 

The load at secondary of T2 is an arc furnace with max load of 850KW.

 

As I know through the seimens hand book that the cap rating for transform is near to the 80-90% of the reactive full load power of the transform. With formula

Qtr = Q0 + Uz/100% (S/Sn) ^2 * S

 

Where Qtr = transformer reactive power, Q0 is the transformer no load power, S = apparent power that a transformer is supplied, Sn = rated power for transformer, Uz is the % impedance of transformer.

 

Here in our case

Q0 from seimens graph = 27 Kvar

S= 1302 for full load

Thus Qtr = 27 + 11/100 (1302/1302)^2 * 1302 = 170KVAR

 

Which is not fulfill in our case, can you suggest me what is the exact relation to calculate the cap bank KVAr and step required to control the p.f in case of transformer, is the bank rating equal to kva rating of transformer?

 

Is there any effect on the secondary voltage of the transform if the cap bank is over rated i.e. if load on transform is reduced?

Link to comment
Share on other sites

Hello tahira

 

A transformer has two components of current flowing, one is the resistive current and the other is the inductive or reactive current. On a single transformer, the reactive, or magnetising current is constant and independant of load. There is an additional reactive component due to the leakage reactance of the transformer, and this does vary with the load. Unlike an induction motor, the dangers associated with over correction are essentially eliminated due to the fact that the transformer does not act as a generator. You can however, get an elevated voltage due to correction but this is not major.

 

With a transformer, I would suggest that you measure the current with the secondary open circuit. This current is essentially magnetisng current and can be fully corrected. As the load is increased, the reactive component will also increase and the power factor will begin to lag. You could add more correction when the load is high, but it depends on how accurate you actually need to be. Automatic correction is probably the best solution for your application, because you are varying the reactive current in the second transformer by varying the voltage.

Your load of an arc furnace will probably have a very poor power factor, not just due to the reactive current, but also due to the distortion of the current waveform. This distortion can not be reduced by the use of power factor correction, so you may still have a poor power factor and high KVA demand.

 

Best regards,

Link to comment
Share on other sites

  • 2 weeks later...
  • 1 year later...

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...