Riyad Posted April 3, 2007 Report Share Posted April 3, 2007 Dear all, I have capacitor banks overloaded morethan 130% (as per IEC). What action shall I take?How to rectify? Kindest regards, Link to comment Share on other sites More sharing options...
marke Posted April 3, 2007 Report Share Posted April 3, 2007 Hello Riyad I assume from your post that you are operating the capacitors with the rated voltage and frequency and under those conditions, the current is more than 130% of the rated current. If this is the case, you have problems with harmonics which will cause the capacitors to fail. The best solution, is to get rid of the harmonics, but this is not always easy, so the next best solution, is to use detuning reactors. If you use detuning reactors, you must:Use capacitors rated for use with detuning reactors. They must be able to sustain a higher voltage continuously. Consult your capacitor supplier.Use detuning reactors rated in the KVAR of the capacitors on each capacitor or bank. It is important that the KVAR rating of the capacitors and detuning reactor match.see http://www.lmphotonics.com/pwrfact.htm Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Riyad Posted April 4, 2007 Author Report Share Posted April 4, 2007 Thank you very much. Appreciate your reply. Hello Riyad I assume from your post that you are operating the capacitors with the rated voltage and frequency and under those conditions, the current is more than 130% of the rated current. If this is the case, you have problems with harmonics which will cause the capacitors to fail. The best solution, is to get rid of the harmonics, but this is not always easy, so the next best solution, is to use detuning reactors. If you use detuning reactors, you must:Use capacitors rated for use with detuning reactors. They must be able to sustain a higher voltage continuously. Consult your capacitor supplier.Use detuning reactors rated in the KVAR of the capacitors on each capacitor or bank. It is important that the KVAR rating of the capacitors and detuning reactor match.see http://www.lmphotonics.com/pwrfact.htm Best regards, Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now