AB2005 Posted June 25, 2007 Report Share Posted June 25, 2007 Dear All, We have a 220KW DC drive for a 220KW, 440V, 1750RPM DC motor which is driving a 2.5meters wide, 60meters long felt in corrugator machine. As I have test run the machine and checked the 3phase current input to the drive 128-133A, checked the DC current out from drive was 120-124A. Is this difference is ok? Can anyone provide me the formula for calculating the 3phase ac current input to drive if we have the value of dc current from drive out put? Thanks for any input. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
gerryroxas Posted June 27, 2007 Report Share Posted June 27, 2007 Hi AB2005, I am trying to figure out how you arrived with that actual measurement. Theoretically: Iac = Sq. root of 2/3 multiplied by Id (Dc current) We may need to start at Power Factor Calculation for SCR Conversion System Power Factor Formula for Three Phase Bridge Rectifying Circuit is as follows: Cos phi. = Power of DC Circuit / Power of AC Circuit = Ed x Id / √3 x Eac x Iac = Ed x Id / √3 x Eac x √2/3 x Id Cos phi. = Ed / √2 Eac Rated Voltage of Ac Circuit = ? Rated Voltage of Dc Circuit = 440 Volts Hence: Cos phi = 440 / √2 x Rated AC Voltage I hope it may assist to start with the calculation, please provide other available information if there’s any. I apologize for poor presentation. I can not “key- in” the Equation Editor Format for numeral. Best Regards, Gerry Link to comment Share on other sites More sharing options...
jraef Posted June 28, 2007 Report Share Posted June 28, 2007 The problem is that because it is a variable speed drive, the output current has virtually no predictable relationship to the input current, because the output voltage will be varying with speed. Why is this important to you anyway? If you need to know the AC current, just measure it at the input side. "He's not dead, he's just pinin' for the fjords!" Link to comment Share on other sites More sharing options...
marke Posted June 29, 2007 Report Share Posted June 29, 2007 Hello AB2005 The difficulty is that i) the AC current in non sinusoidal and so the average current will be different from the RMS current. This means that the way that you measure the current will strongly influence the AC current measurements. ii) The ratio between the AC current and the DC current is a function of the conduction angles of the controlled bridge. I expect that you will find different meters giving you different answers on the AC current measurement with the errors increasing as the DC voltage is reduced. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
AB2005 Posted July 8, 2007 Author Report Share Posted July 8, 2007 I expect that you will find different meters giving you different answers on the AC current measurement with the errors increasing as the DC voltage is reduced. Yes Marke. You are right. I have measured the current with two different meters and found the different answers. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...