tahira Posted November 30, 2002 Report Share Posted November 30, 2002 Hi gents! We are recently working on a substation having 132/11kV system with 36MVA transformer (Y-Y with treasery winding). There are differential, O/C, U/V, O/V, E/F and all other transformer protections is there with individual protection for different feeders (S/C, E/F, O/C). I have following quires: 1. What is the difference b/w unrestricted and restricted earth fault protection, how they differ and what are there selecting criteria according to application, which one provided more accurate and complete protection?2. What is the setting procedure for differential protection?3. Selection criteria of protection relays setting i.e. O/V, U/V, O/C and S/C.4. What is directional O/C relay, how they differ from no directional relay, is there any advantage for using directional relay? 5. Plz info me any web site given me details about protection relays (cables feeder protection, …)?6. Is any one having info about E-Tap software? Best regards ASD Link to comment Share on other sites More sharing options...
jackson8000 Posted January 19, 2003 Report Share Posted January 19, 2003 Hello tahira, Regarding item #6, ETAP software is very good. We use it exclusively for analysis, coordination, etc. You can find it at www.etap.com. Good luck. Link to comment Share on other sites More sharing options...
RalphChristie Posted March 21, 2003 Report Share Posted March 21, 2003 I would suggest that you visit following sites http://www.geindustrial.com/pm/notes/artsci/ - go to transformer protectionhttp://www.selinc.com/techpprs.htmhttp://www.ee.polyu.edu.hk/staff/eekkli/BE.../Ch3_OC2003.pdf - very good - about relayinghttp://www.usace.army.mil/inet/usace-docs/...ytm/tm5-811-14/ http://www.relaylounge.com/servlet/Content...id=987664718399For last one you have to register (free) - then go to NPAG relay technology It is a lot of places - but there is good information Good luckRCC Link to comment Share on other sites More sharing options...
sethar Posted August 22, 2003 Report Share Posted August 22, 2003 Hello tahira, 1. Unrestricted earth fault is used for feeder protection,not for limited zone & less sensitive. Restricted earth fault is used for transformer protection ,it is also called ground diffrential & limited to zone , not will trip beyond the zone.Restricted is more accurate protection.2. Setting procedure of diffrential depends on both side Pri/Sec current & CT ratio ( Suppose in case of transformer Delta to Star) Star side I = 1600 A & CT is 2000/1Delta side I = 52 A & CT is 75/11600/2000=base current52/75=base currentthose settings intered into relay includind system parametersactually diffrential relay sense ratio/deffrence between both side in term of % according to settings + error in base current ratio, in this relay no any time setting is required it take action on immediate effect as sense diffrence.3. Selection criteria of protection relays depends system designe/load/criticality /as per current carrying capacity of equipment/short ckt values/i.e down stream side settings should be lower than up stream side.4. Directional relay is better than withour directional relay it woks/sense through one direction only. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now