AB2005 Posted August 25, 2007 Report Share Posted August 25, 2007 Dear all I have some confusion for calculating the active and reactive power. I have a flood light with ballast 400W, 220V, Cosф 0.45. I calculated a capacitor 44uf for PF improvement upto 0.96 but available capacitor was 50uf. first I checked the current of light before PFC was 3.4A. I connected the capacitor then checked and found the following; Current in main line (from switch to light) = 2A Current in out going cable from capacitor = 2.3A Current at light terminals = 3.4A I couldn’t understand that why the current difference? 2 + 2.3 = 4.3A but we have 3.4A at light terminals. how can we calculate these figures. I think I am missing some thing. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
marke Posted August 25, 2007 Report Share Posted August 25, 2007 hello AB2005 You can not add the currents together. The current into the capacitor is at phase quadrature to a resistive current. It is a capacitive current. The current into the lamp is a vector made up of resistive current, and inductive current. The current in the supply is a combination of the resistive component of the lamp current and the inductive current of the ballast and the capacitive current of the capacitor. If you break the lamp current down to ists resistive component and it's inductive component, then you can subtract the inductive component and the capacitive component to end up with a resultant reactive current. The you square the reactive current and square the resistive current, add these together and take the square root to get the supply current. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
AB2005 Posted August 27, 2007 Author Report Share Posted August 27, 2007 Thanks Mark for your valuable comments. Now we have the values of current Im=2A at main cable, Ic=2.4A at capacitor out put and Il=3.4A at lamp cable. How can we calculate the both currents Im and Ic while capacitor is 50uf? "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now