I undertand that different reduced starters are constant voltage or constant impedence or constant current starters, but what I don't understand is how that affects the motors current and torque. Best I can figure is that a constant impedence starter means that if you reduce the voltage the current also reduces. I need to understand the same for all three type of starters.
Link to comment
Share on other sites

Hello TCE

 

Welcome to the forum.

 

At any time during the start, the torque produced by the motor is a function of the full voltage torque at that speed, and the square of the current being used to start the motor.

 

The motor has an impedance which is a function of the motor design and the speed of the rotor.

 

If you reduce the voltage applied to the motor, you will reduce the current. (I = V/Z)

 

If you apply a constant reduced voltage to the motor during start, you can easily calculate the start current and torque curves from the full voltage curves.

Likewise, if you apply a constant current start to the motor, you can also calculate the start torque curves from the full voltage current and torque curves. With a constant current start, the terminal voltage, is a function of the start current and the motor impedance which rises as the motor increases in speed.

 

If you apply a constant impedance starter, then the voltage at the motor terminals at any speed is going to be a function of your starter impedance and the motor impedance which is a function of motor speed. As the motor accelerates, the motor impedance increases, so the motor terminal voltage increases.

 

Best regards,