Hello Rahul

 

As you increase the load on an induction motor, the motor slows a little. This is due to the increase in slip. There must be an increase in slip in order to increase the torque produced by the motor.

With some drives, there is a function called slip compensation. This causes the drive frequency to rise a little as the load is increased in a manner that the motor speed becomes less load dependent. This is called slip compensation.

For example, if we have a motor that has a full load slip of 3%, and we can adjust the slip compensation to increase the frequency by 3% at full load, the slip will equal the frequency increase.

 

Best regards,

Link to comment
Share on other sites

Hello Rahul

 

As you increase the load on an induction motor, the motor slows a little. This is due to the increase in slip. There must be an increase in slip in order to increase the torque produced by the motor.

With some drives, there is a function called slip compensation. This causes the drive frequency to rise a little as the load is increased in a manner that the motor speed becomes less load dependent. This is called slip compensation.

For example, if we have a motor that has a full load slip of 3%, and we can adjust the slip compensation to increase the frequency by 3% at full load, the slip will equal the frequency increase.

 

Best regards,

 

Thanks marke

 

for quick reply.

 

take care

 

Regards

 

Rahul

 