Ramasubramanian Posted November 30, 2007 Report Share Posted November 30, 2007 Dear Friends, A 15kw motor driven hoist is connected through a VFD. The application being tough we had connected VFD of capacity 18.5kw and started using the hoist. It takes a load of 3 ton and beyond it does not hold the load. What is the reason for that. Some one says that it has to be used with Dynamic Breaking Unit and DB Resistor. Please explain. Link to comment Share on other sites More sharing options...
anu_rags Posted November 30, 2007 Report Share Posted November 30, 2007 In hoist application, regeneration takes place from the motor side while lifting. Therefore the DC voltage will increase till a limit and then the VFD will trip under DC bus overvoltage. In order to dissipate this excess energy, Brake Chopper and Resistor is required. You need to size the DBR as per your application requirement. Regards, Anurag Link to comment Share on other sites More sharing options...
Ramasubramanian Posted December 4, 2007 Author Report Share Posted December 4, 2007 Drive for hoist applicationIn hoist application, regeneration takes place from the motor side while lifting. Therefore the DC voltage will increase till a limit and then the VFD will trip under DC bus overvoltage. In order to dissipate this excess energy, Brake Chopper and Resistor is required. You need to size the DBR as per your application requirement. Regards, Anurag Link to comment Share on other sites More sharing options...
marke Posted December 4, 2007 Report Share Posted December 4, 2007 Hello Ramasubramanian Can you give us more detail on the problem that you are having. beyond it does not hold the load Do you mean that it will not hold the load stationary, or that it will not lift the load, or it will not lower the load in a controlled fashion? There are a number of scenarios and if you can give us more detail, it will be easier to give you a meaningful answer. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now