bob Posted December 11, 2007 Report Share Posted December 11, 2007 Hi, I hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options 1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power. or 2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding. I need only around 600 k W for my application. Am i following the right path. Bob Link to comment Share on other sites More sharing options...
subrao Posted December 11, 2007 Report Share Posted December 11, 2007 Dear Bob, You are definitely following right path 1.Out put Kw is propotional to square of voltage.So when you apply only 5.5Kv you get 25% of 1MW that is 250KW 2. If you connect the motor in delta and apply 5.5 kV you get 3 times more out put namely 750KW At the same time you have to take care of rotor volts which will be 50% in first case and 86% in second case while deciding starting resistances in rotor circuit subrao Hi, hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options 1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power. or 2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding. I need only around 600 k W for my application. Am i following the right path. Bob Link to comment Share on other sites More sharing options...
marke Posted December 11, 2007 Report Share Posted December 11, 2007 Hi Bob I agree with Subrao. Good information, and the note on the rotor is certainly one to watch out for. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
bob Posted December 13, 2007 Author Report Share Posted December 13, 2007 Hello Marke, Torque is proportionl to the square of the voltage but does it hold true for power also ? Regards. Bob Link to comment Share on other sites More sharing options...
marke Posted December 13, 2007 Report Share Posted December 13, 2007 Hello Bob Power equals Torque times Speed times a constant, so at a constant speed, the power is directly proportional to the speed. So yes, at a given speed, power is proportional to the square of the voltage. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...