Operating At Slightly Lower Rated Voltage


bob

Recommended Posts

Hi,

 

I hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options

 

1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power.

or

2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding.

 

I need only around 600 k W for my application.

 

Am i following the right path.

 

Bob

Link to comment
Share on other sites

 

Dear Bob,

 

You are definitely following right path

1.Out put Kw is propotional to square of voltage.So when you apply only 5.5Kv you get

25% of 1MW that is 250KW

 

2. If you connect the motor in delta and apply 5.5 kV you get 3 times more out put namely 750KW

 

At the same time you have to take care of rotor volts which will be 50% in first case and 86% in second case while deciding starting resistances in rotor circuit

 

subrao

 

 

 

 

Hi,

 

hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options

 

1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power.

or

2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding.

 

I need only around 600 k W for my application.

 

Am i following the right path.

 

Bob

Link to comment
Share on other sites

Hi Bob

 

I agree with Subrao. Good information, and the note on the rotor is certainly one to watch out for.

 

Best regards,

Link to comment
Share on other sites

Hello Bob

 

Power equals Torque times Speed times a constant, so at a constant speed, the power is directly proportional to the speed.

 

So yes, at a given speed, power is proportional to the square of the voltage.

 

Best regards,