marke Posted December 31, 2007 Report Share Posted December 31, 2007 One of the areas that I operate in, has a high density of VFDs on pumps on relatively weak supplies. The result is that the high levels of harmonics on the VFD inputs has accumulate in the supply and is causing a high THD of the supply voltage. While we do have supply regulations covering harmonics, in this instance, the harmonics are higher than they should be. There is an option of using zig zag transformers and six phase rectifiers as a means of reducing the harmonics drawn by drives however in this case, the drives are already installed. There is a transformer for each drive and sizes range up to 200KW. One thought that I had, was that for future installations, and there are new installations going in all the time, that the new supply transformers be designed with a zig or a zag winding to give a phase shift, and install equal loading on the leading and lagging phase shifts. This should act like a twelve pulse input on one drive, only it will be across two drives. Any thoughts on this?? Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
mariomaggi Posted January 1, 2008 Report Share Posted January 1, 2008 Dear Marke, happy new year - first of all. Your solution is valid if both drives are energized together, otherwise you will lose the benefit. If local rules are not so stringent, it is possible to use this solution, accepting to have more harmonics when one load is disconnected. Regards Mario Mario Maggi - Italy - http://www.evlist.it - https://www.axu.it Link to comment Share on other sites More sharing options...
marke Posted January 1, 2008 Author Report Share Posted January 1, 2008 Hi Mario Compliments of the season to you also. This region has around 2000 VFDs installed at present and the harmonics are high. New VFDs are going in daily, so my though was to recommend phase shift transformers for all new installations and this would over time help to reduce harmonic levels, which is probably a better solution that installing future drives with filters etc and leave existing harmonics in place. Drives are for controlling irrigation pumps and there is one transformer per pump, so it is practical to do and all drives tend to run at the same time. Have a good day, Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
anu_rags Posted January 2, 2008 Report Share Posted January 2, 2008 Hi Mark, At one such place, we were required to provide drives that meet IEEE519 standards for current and voltage. We had 4 no drives of equal size. A 12 pulse drive wont have been able to match the harmonics standards. We were looking for a phase shifting transformer for quase 24 pulse system with 6pulse drives. I was not able to find any suitable manufacturer of such transformers. Have you come across any such trafo? Regards, Anurag Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now