andym79 Posted February 9, 2008 Report Share Posted February 9, 2008 Hi I am trying to learn as much as I can about motors and starters! I have a question, what can make the the overloads operate when a star delta three phase motor starts? Link to comment Share on other sites More sharing options...
marke Posted February 9, 2008 Report Share Posted February 9, 2008 Hello andym79 When a motor is started, it draws a very high current for the duration of the start period. The actual current and length of start time is a function of the motor design, the load torque and inertia and the starting method used, but under full voltage starting conditions, the start current will typically be between 550% and 900% of the motor rating. This overload current will cause a temperature rise in the motor and also a temperature rise in the thermal model employed by the overload relay. If the overload relay thinks that th motor is too hot, it will trip. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
andym79 Posted February 10, 2008 Author Report Share Posted February 10, 2008 Thanks, Is it also right that overload relays can also operate due to an earth fault, undercurrent and phase imbalance? Or am I confusing my self, as on start up overload/overcurrent is the likely cause? Link to comment Share on other sites More sharing options...
chris1373 Posted February 12, 2008 Report Share Posted February 12, 2008 Hi, as i know, overload relays will operate every time that the seting current is overpassed. The thermal protection in a overload relay will act following a curve, so if the current is not to high, it will take a time to act. The magnetic protection act inmediatley wehn a fault occurs, like an earth fault. Chris. Thanks, Is it also right that overload relays can also operate due to an earth fault, undercurrent and phase imbalance? Or am I confusing my self, as on start up overload/overcurrent is the likely cause? Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now