emms Posted February 17, 2008 Report Share Posted February 17, 2008 I amusing a 112kw slip ring induction motot on a crane hoist. The motor failed and upon investigation, we found a damaged cable and the rotor had developed a short circuit between phases. The dilemma is, we have a short circuit on the rotor, and the supply is tripping on earth fault, instead of overload as I have expected. I cant explain that! Link to comment Share on other sites More sharing options...
marke Posted February 18, 2008 Report Share Posted February 18, 2008 Hello emms Welcome to the forum. It sounds to me as though you have tow faults, one on the stator and one on the rotor. I would not expect a rotor problem to bring up an earth fault unless there is an earth connection in the starter also and the earth fault is derived by monitoring the current flowing in the earth conductor. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
spkam Posted March 21, 2008 Report Share Posted March 21, 2008 Dear all We may consider motor as a rotating transformer , with air gap as the flux tranfer medium Now if a secondary earthfault in a transformer can reflect in the primary , why not in a motor+++ provided the stator winding is star connected ????? Kamath Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now