Hello Jan

 

welcome to the forum.

pfc capacitors are used to improve the power factor of induction motors and thereby reuce any power factor or KVA penalty that you may be paying. They will not reduce the kw drawn by the motor. If you use a vsd, you can not use pfc capacitors. pfc capacitors across the motor will cause the vsd and/or the capacitors to fail! You must use either one or the other but not both.

 

Best regards,

Link to comment
Share on other sites

Hello Jan

 

To give you a definative answer, we would need to have a lot more information.

Fitting a VSD will only save energy if you are going to operate the motor at reduced speed. I would expect that this is not the case in this application, so you could actually end up using more energy by fitting the VSD.

Yes, you can use a VSD and still have bulk correction at the point of supply, but the input current to the VSD is very rich in harmonic currents and could cause an increase in the capacitor current and premature capacitor failure. I would recommend that if you are using bulk correction on the same supply as you have VSDs connected, that you fit detuning inductors to the capacitors.

Best regards,

Link to comment
Share on other sites

  • 7 months later...

Hello Daniel

 

The reactor is an inductor, so yes they are the same thing.

 

Best regards,

Link to comment
Share on other sites

  • 3 months later...

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...