DanNguy Posted December 17, 2008 Report Share Posted December 17, 2008 Hello, Is it a good pratice to install an PFC with detuned reactor and active harmonic filter simultanuously? Please advise. Regards, Dan Link to comment Share on other sites More sharing options...
marke Posted February 1, 2009 Report Share Posted February 1, 2009 Hello Dan I would not consider it necessary to add both power factor correction and an active harmonic filter as the active harmonic filter would generally correct the power factor also. If you have a significant displacement power factor problem as well as a harmonic power factor problem, then it may be worth considering the use of both capacitors and the active filter. Before doing this, I would recommend that you contact the filter supplier to ensure that the filter is not going to be adversly affected by the capacitors. Best regards, Mark. Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...