Dear All,

 

I need some urgent help for selecting Softstarter for Centrifugal compressor application. Im attaching the load torque curve of the compressor. http://rapidshare.com/files/181073531/win6...Curve_50_Hz.pdf. Starting time required for the compressor is 5-12 seconds.

 

Motor details are AMbient temp = 45 deg c

Motor rating = 410 KW

Operating volt = 415 +/- 10%, 3 ph, 50 Hz +/- 3%

Full load current = 650 A

 

I have selected Emotron Softstarter of 500kw rating, 710A current with 300% overload for 30 sec. Will this be suitable for this compressor? How do we determine from the load torque curve of compressor, that it can be started with a softstarter? Presently he is using FCMA type starter and want to switch to SCR soft starter.

 

Regards,

Anurag

Link to comment
Share on other sites

Hello Anurag

 

First, yes you can use a soft starter to start this compressor, but the start current is a function of the speed/torque curve of the compressor and the speed/torque and speed/current curves of the motor.

 

There are major variations between the start characteristics of motors and the start current variation for a given load can vary by more that 50% depending on the motor.

 

Do you have any data on the motor? I would need this to comment. Without this data, I would allow for a start current of 400 - 450% from my experience.

 

Best regards,

Mark.