WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).

Sometimes this MCCB is tripping .But no trip in DB MCB.

Can anybody tell me reason ?

From where i can know about the MCCB settings?

Link to comment
Share on other sites

  • 4 months later...
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).

Sometimes this MCCB is tripping .But no trip in DB MCB.

Can anybody tell me reason ?

From where i can know about the MCCB settings?

 

do you have current injector ?

 

if you do, you may test the mccb by injecting 63A.

Link to comment
Share on other sites

  • 2 months later...
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).

Sometimes this MCCB is tripping .But no trip in DB MCB.

Can anybody tell me reason ?

From where i can know about the MCCB settings?

 

 

there could be many reasons for tripping

1 if the cummulative output current (all lights and sockets etc) exceeds 63 amps

2 if your had a circuit that required a large inrush current (motor or transformer etc)

3