Normally the soft starter manufacturers claims for Energy save with their decise ! and may be effective when motor is underloaded appx 40% but in a case where motor is 80 % loaded and working with full efficiency .

 

Do enebling of Energy save is advisable ? Will the device work as energy saver or more as a Losser ....... as it increase in Harmonics distortions in line as signal no more remains pure sine what will be ratio for Cu losses , Iron Losses , Windage losses compared to the wastage energy saved ..........

Link to comment
Share on other sites

Hi Niranjan,

 

If a motor is loaded at 80% then the opportunity for saving energy will be small.

 

There will be a slight amount of harmonic distortion but this is small, the added loses for the soft starters are generally 1 Watt per Amp per Phase.

 

To negate these affect a bypass contactor could be used.

 

Thanks

 

Steve

Link to comment
Share on other sites

Hello Niranjan

 

The energy saver only reduces the magnetising losses in the motor and this only works when the total current is close to the magnetising current of the motor.

Only use this feature if the motor a) has high magnetising losses, and B) if the motor operates for a significant period of time under idle conditions.

See http://www.LMPhotonics.com/energy.htm

 