AB2005 Posted April 24, 2010 Report Share Posted April 24, 2010 Dear Friends, As we know that the improvement in power factor effects on looses in power source, cables, bus bars etc due reactive current passing. Does it also effect on fuel economy of generator? "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
marke Posted April 24, 2010 Report Share Posted April 24, 2010 Hi AB2005 Adding power factor corection will reduce the current drawn if you have a poor displacement power factor. This in turn will also reduce the losses in the alternator and in the distribution system. The engine produces KW, not Amps. The reduction in KW will reduce the fuel, but not the reduction in amps. Best regards, Mark. Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
AB2005 Posted April 27, 2010 Author Report Share Posted April 27, 2010 Thanks Mark OK. It means that correcting of PF only increases the capacity of distribution system not the power supply source i.e. Generator or Transformer. Am I right? There is a little confusion which must be cleared. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
marke Posted April 28, 2010 Report Share Posted April 28, 2010 Hello AB2005 The generator set comprises an engine and an alternator. The engine develops KW and the alternator develops KVA. Power factor correction reduces KVA and to a much lesser extent KW. You may halve your KVA and only reduce the KW by 10%. The alternator and the transformer are loaded by KVA. If you have a poor power factor, then the maximum KW that you can load up a transformer or alternator with is reduced. A 750KVA transsformer can carry 750KW with a power factor of 1.0, but only 375KW with a power factor of 0.5. The same applies to a 750KVA generator set. If you have a 750KVA generator with a power factor of 0.5, you can only apply 375KW of load. The alternator is fully loaded, and the engine is only half loaded. Best regards, Mark. Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
AB2005 Posted April 30, 2010 Author Report Share Posted April 30, 2010 Excellent! Thanks Mark. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...