SGK2007 Posted August 12, 2010 Report Share Posted August 12, 2010 I have a few querries: 1. Is the earth fault current setting in an MPR same as the actual flowing current in the CBCT primary, that is the current that flows in armour of the cable. 2.What is the locked rotor setting for star delta starting of motors to be provided. The default setting in the MPR is 7times Link to comment Share on other sites More sharing options...
marke Posted August 14, 2010 Report Share Posted August 14, 2010 Hello SKG2007 1) sometimes 2) I would set equal to the DOL setting as when the starter changes to delta, the MPR ses the delta impedance. Ideally, you would have a star setting and a delta setting. Best regards, Mark. Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...