Typically using a VFD to run a motor above the nominal frequency will result in lost of torque as the maximum frequency is exceeded. I just want to know if its ok to run the motor above the rated frequency using direct torque control or is scalar a better option?

How does this impact on motors with rating of up to 120 hz also on the nameplate?

Link to comment
Share on other sites

Typically using a VFD to run a motor above the nominal frequency will result in lost of torque as the maximum frequency is exceeded. I just want to know if its ok to run the motor above the rated frequency using direct torque control or is scalar a better option?

How does this impact on motors with rating of up to 120 hz also on the nameplate?

 

 

It would be helpful if you were to provide specific information so that a reply could be constructed that applies to your application and issues.

 

To that end ... please provide:

  • COMPLETE motor nameplate (rating plate) data
  • Describe application
  • Manufacturer of VFD
  • Model Number of VFD
Link to comment
Share on other sites

It would be helpful if you were to provide specific information so that a reply could be constructed that applies to your application and issues.

 

To that end ... please provide:

  • COMPLETE motor nameplate (rating plate) data
  • Describe application
  • Manufacturer of VFD
  • Model Number of VFD

 

 

Ok its an ABB ACS800 drive used to operate a 20 hp 460V motor for a gas compressor(VRU). The motor current is 22.7 A, for the frequency the nominal value is 60 hz but there are other frequency rating on the nameplate. That is 3-60hz, 6-60hz and 60-120hz.

Link to comment
Share on other sites

Ok its an ABB ACS800 drive used to operate a 20 hp 460V motor for a gas compressor(VRU). The motor current is 22.7 A, for the frequency the nominal value is 60 hz but there are other frequency rating on the nameplate. That is 3-60hz, 6-60hz and 60-120hz.

 

 

 

  • COMPLETE motor nameplate (rating plate) data

 

 

Is compressor of the Positive Displacement type, or the Centrifugal type ?

Link to comment
Share on other sites

It's positive displacement

 

 

Thank you for reply.

 

 

Further evaluation/analysis of your Constant Torque application required to answer your questions originally stated.

 

Please supply ..... C o m p l e t e ...... motor nameplate data as previously requested.

 

 

Thank you.

 

/