honeywell Posted February 24, 2004 Report Share Posted February 24, 2004 I have a motor connected to a pump for low pressure hot water (62 dec c) on the data plate the motor says 400V 50Hz 1450 rpm 7.5Kw 0.82cos 15.20 amps delta connection. But when I connect my clamp on amp meter the current drawn is 18 amps why is this when the motor is rated at 15.20 amps is this rating not true power?? Thanks for any help Paul Kav Honeywell Controls Link to comment Share on other sites More sharing options...
marke Posted February 25, 2004 Report Share Posted February 25, 2004 Hi Paul I would not continue to run the motor under those conditions. The motor is probably undersized for the pump.The current on the nameplate, is the highest current that you should run the motor continuously. Operation at a higher current will result in increased heating and therefore a premature failure. You can reduce the load on the motor by reducing the flow of the hot water. This can be achieved by slighlty closing a valve on the outlet of the pump, or by fitting an orrifice plate on the output of the pump. (this will increase the pressure seen by the pump and reduce the flow, reducing the power drawn from the motor. If the pump is not a centrifugal design, then you may need to slow it down to reduce the loading. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now