Dear Sirs,


please look into my problem and help me. We have one MCC with Main Incomer MCCB and 3 Soft Starters in Outgoing side with Individual Outgoing Breakers. There is one Capacitor bank also controlled by dedicated Power Factor Regulator.


​At the Motor starting (Any one out of the three) incomer Current in the digital Meter and Outgoing Current in the Digital merter Installed in the soft starter circuits are Same at 0.75 power factor Incomer and Outgoing Currents are 84A- L1, L2,L3. But after Power Factor correction PF - 1, Incomer Current is falling to 64A- L1, L2,L3 but the Outgoing Soft starter current is still 84A- L1, L2,L3.


​Can anyone help me please, we have checked the CT and measured the current with separate Clamp Meter also, again the scenario is the same.


Please reply me

Abhilash, abhi.mureeckal@gmail.com

Link to comment
Share on other sites

hello amb2000

 

The current drawn by a motor comprises a resistive component and an inductive component.

 

The resistive component is in phase with the voltage and the inductive component is 90 degrees behind the voltage.

The current measured is the vector sum of both the resistive and inductive currents.

 

Power factor correction uses capacitors to draw capacitive current which leads the voltage.

The capacitive current is 180 degrees out of phase with the inductive current and can be used to cancel the inductive current.

 

With power factor correction installed, the current into the motor is the resistive current and the inductive current. There is no change resulting from the addition of the pf correction.

 

The current drawn from the supply is the current into the motor plus the capacitive current.

If the capacitive current is equal to the inductive current, the inductive current is cancelled from the supply, so the net current is reduced.

This is the whole role of pf correction.

 

Best regards

Mark

Link to comment
Share on other sites

hello amb2000

 

The current drawn by a motor comprises a resistive component and an inductive component.

 

The resistive component is in phase with the voltage and the inductive component is 90 degrees behind the voltage.

The current measured is the vector sum of both the resistive and inductive currents.

 

Power factor correction uses capacitors to draw capacitive current which leads the voltage.

The capacitive current is 180 degrees out of phase with the inductive current and can be used to cancel the inductive current.

 

With power factor correction installed, the current into the motor is the resistive current and the inductive current. There is no change resulting from the addition of the pf correction.

 

The current drawn from the supply is the current into the motor plus the capacitive current.

If the capacitive current is equal to the inductive current, the inductive current is cancelled from the supply, so the net current is reduced.

This is the whole role of pf correction.

 

Best regards

Mark

Hello Mark,

 

Thanks for your kind support, Just need to check with you few things,

1) Is there any possibility of making both the currents the same. How we can reduce the current in the Outgoing side of Soft Starter as we cannot connect the capacitors in the Outgoing side.

2) Is this the same scenario in all the circuits where ever SoftStarters and Drives are coming along with Capacitor banks.

3) Can I advise my customer, our system is working perfectly and there is no problem to worry in this regard.

 

Please reply me

Abhilash

Link to comment
Share on other sites

Hello Abhilash

 

1) If you measure the current at the actual input and output of the soft starter, you will find that they are equal. The current is only reduced on the line side of the PFC connection.
2) Any system that has power factor correction will (should) show a reduced current on the line side of the power factor correction connection point.

In the case of VFDs, you do not apply power factor correction capacitors because the displacement power factor is already better than 0.95 The true power factor will typically be much less because the harmonic power factor is less than 0.95

3) Definitely!!

 

Best regards,

Mark

Link to comment
Share on other sites

Dear Mark,

 

Kindly note for above Point 1 , I would like to share the single line diagram for more clarity. Please go through this and advise, Soft Starter Line side and the Capacitor bank connection points are the same here. Then why there is difference in current in both Ammeters.

 

Can you please check.

Abhilash