Guest Posted July 21, 2004 Report Share Posted July 21, 2004 The busbar rating given seems to be for a single busbar in free air.Is there a way to find ratings for multiple busbars,i.e. three100x10 in parallel per phase, A) unenclosed enclosed C) insulated for A) or above Link to comment Share on other sites More sharing options...
marke Posted August 1, 2004 Report Share Posted August 1, 2004 That is correct, the ratigs are for free air only. You must derate for restricted airflow. The difficulty is just how to define the restricted airflow so that a derating can be applied.There are numerous rules of thumb that have been applied in the industry for certain conditions, but the best thing to do, is to create the environment and make temperature rise measurements. When putting busbars in parallel, it is necessary to derate to ensure that the current sharing imbalance does not cause overheating of one bar, or one point in a bar. I would normally derate by 10 - 20%. The amount of dertaing is also dependent on the spacing between the busbars. If they are very close, you will restrict the airflow between the bars and a greater derating will be required. Best regards, Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now