AB2005 Posted May 30, 2018 Report Share Posted May 30, 2018 Hi;I want to control the speed of 3 single phase motors each 120W by a 3phase inverter drive. In this case, the motors will be connected in star connection. How about this idea? Please share your experience. "Don't assume any thing, always check/ask and clear yourself". Link to comment Share on other sites More sharing options...
marke Posted May 30, 2018 Report Share Posted May 30, 2018 Hello AB2005 If the three motors are identical, and all operate at the same time, and at the same load, and are shaded pole motors, then this will work fine.If the motors have a start winding along with a start switch to connect and disconnect that winding, then the impedance will be so variable, that the voltage applied to each motor will change and there will be issues. It works well for shaded pole fan motors, but some of these motors do not like the PWM waveform and can overheat with increased slip losses. There is a VFD designed for use with single phase motors, you would need one VFD per motor. Best regards,Mark Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...